    Good Morning Guys and Gals;
    I'm have some issues with my servo drive setup and need some guidance. I've completed two
    other cnc projects and this is the first time with these issues. I may be asking too much of
    my machine but here goes!!!!
    Machine is a home built router 34"X34" with .2" lead ball screws. The axis are all on bearing
    trollys and all mechanical movement is bind free. My drive system is as follows:
    3 each Gecko 320
    2 each ElectroCraft E643 (X&Z) Nema 34, 90V Max 4800 RPM motors.
    1 each Electrocraft E712 (Y) Nema 34, 60V Max 2100 RPM motor.
    BOB is a PMDX-126 wired as the manual describes for Gecko Monitoring (stop on fault).
    Power supply is a home built high amperage torroidal design with filter cap and diode. Max
    voltage is 52V DC.
    The motors are belt coupled with a 1:1 ratio.
    Control computer is a dell 2Ghz with 1 gig of memory and dedicated to the machine.
    Running mach 3 at 45000 Hz
    Motors are tuned at an acceleration of 8 (z) and 10 (x&Y).
    System was calibrated using a digital caliper and the built in Mach calibration feature.
    Motor Speed!!!
    Thats the issue. I can't get the sytem to run past 70 ipm without faulting. I was targeting
    150 ipm on rapids. The fault occurs when the drives reverse.
    I've attempted to tune the geckos with a scope but can't figure how to hook set up the scope
    and have it resemble anything in the documentation. I've tuned the system by ear many many
    times. I'm almost afraid I'm wearing out the pots!
    One test that I conducted this weekend kind had strange results.
    What I was attempting was to test the PMDX 126 gecko monitoring feature. I loaded some code
    and started the machine cutting air. I then removed the HV fuse on the motor side of the gecko
    for the y axis. The position error was noted and the machine faulted and stopped mach. Just
    like it is suppose to work.
    I then replaced the fuse, restarted the program and removed the x fuse. The gecko did not
    fault until I tried to replace the fuse. Strange. I replaced the fuse and started the system
    again. I then removed the z fuse and the system just kept on running. I replaced the fuse and
    the axis started working again but of course it was out of position. Almost like the gecko
    position error monitoring feature was not working.
    I then tried to test the position error circuit (encoder) as is suggested in the 320 manual. I
    connected a vom to the test pins and 5 volts was noted. Of course to move the motor/encoder
    out of position, I had to remove the hv from the sytsem, otherwise the motor cannot be turned
    due to motor torque. Well, the 5 volts is no longer present when the hv is removed, even
    without turning the motor. I guess the 5V is supplied from the hV circuit.
    After reading all the above, I kind of realize that the motors are badly mismatched with a 60 v
    motor on the y and a 90v motor on the x and z. Will this make a difference?
    One other bit of information. I checked the voltate on the motor output from the geckos when
    doing a rapid movement at 100 ipm and the voltage was only 7 - 8 volts. I haven't done the
    math but the power supply is most definately capable of that. Will the low voltage demand
    impact the error monitoring feature in the gecko?
    Any thoughts or help will be very appreciated.
    I'd like to get 150 ipm out of this system but reliability is the most important!
    HELP.
    Bill
    Oh yeah, sorry for the long post but I've been working on this crazy system since Christmas!
    billyjack
    Helicopter def. = Bunch of spare parts flying in close formation! USAF 1974 ;>)
    Apr 2004
    VA, USA
    Help with G320X
    Hi Bill,
    The tuning of servo systems is a process that can cause
    plenty of frustration.
    The G320X instructions describe the P, I, and D adjustments,
    but there are other factors that can be used to affect
    the servo response.
    First is the encoder resolution. If you are using the
    AMT-102 style encoders, you can set dip switches internal
    to the encoder to control the resolution. You should set
    only as much resolution as you need. For example you will
    want the encoder feedback to offer between 4 and 10 times
    as much resolution as the minimum commanded movement that
    you need to achieve. Excess resolution can offer tighter
    performance, but may also make it more difficult to tune
    your system. There is also the possibility that high resolution
    settings could require pulses faster than you computer can
    generate them.
    Remember that the G320X will use quadrature decoding, so
    if your encoder offers 500 pulses per revolution, then
    the G320X will be able to see 2000 counts per revolution.
    The G320X following error detection circuitry has an
    adjustable limit. If your servos struggle to maintain
    tight following when moving fast, and you really only
    need tight precision when moving slow, then you can
    set the DIP switches (number 4 and 5) to allow greater
    following error before signaling a fault.
    The G320X also has adjustable torque gain. For most
    users the default setting works, but sometimes you may
    benefit from changing the setting of DIP switches
    8, 9, and 10. This will affect the feedback stability.
    Lastly, the G320X has a current limit adjustment. If
    this is set lower than required by the motor specifications,
    it can limit the amount of torque available unnecessarily.
    Simulating a fault by removing the fuse is not a valid
    approach. The G320X cannot monitor position and provide
    fault detection when it does not have power.
    The best way to simulate faults is to mechanically
    overpower the servo motor so that it is out of position.
    You can also connect a momentary switch between the
    ERR/RES (terminal 5) and Encoder +5VDC (terminal 7).
    This will cause all the G320X drivers that have their
    ERR/RES terminals connected together to enter the fault
    state.
    This simulated fault will cause the G320X drivers to stop
    driving the motors, and cause the PMDX-126 to signal an
    E-Stop to Mach3. When you then click on the flashing RESET
    on the Mach3 screen, the PMDX-126 will reset the G320X
    drivers and they will again begin driving the motors.
    If you click on the RESET on the MACH3 screen when
    the drives have not signaled a fault, the PMDX-126
    will NOT disable the drives. This was a design decision
    to allow the user to reset Mach without causing the drives
    to freewheel if there had not been an E-Stop.
    Measuring the voltage to the motors, assuming that
    your meter is not confused by the PWM square wave
    signal, will tell you how fast the motor should be
    trying to turn. It is quite possible to develop full
    torque with less that 10 volts applied if the motor is
    moving slowly relative to its rated speed. For DC
    brush type servo motors, speed will be related to
    voltage, and torque will be related to current.
    The following error detection circuit and the encoder
    are powered by the V+ motor supply voltage on terminal 2,
    but should operate correctly at any voltage above 18 volts.
    The actual voltage should not influence the error detect
    sensitivity.
    Having a lower motor supply voltage will limit the top
    speed of you motor, but my guess is that your supply
    voltage is not your problem. Even running at half speed
    your motors will probably drive your machine at much
    faster speed than you are trying to achieve. Do the
    math keeping in mind that motor speed is revolutions
    per minute and machine travel speeds are also in inches
    per minute. Don't get tripped up inserting a factor of
    60 somewhere.
    Hope this give you some ideas without confusing things
    even more.
    Regards,
    Steve Stallings
    www.PMDX.com
    Apr 2005
    Thanks Steve;
    This is all good information and I now understand how the PMDX board works much better. Unfortunately, the other information relative to the Geckos will not help very much since I have the 320's and not the 320x. There are no selectable attributes only the pots to set. Thus the reason I cannot understand why I can't find a "magic" sweetspot after all my tuning. Basically, there are only two adjustments required and I can't seem to find the correct combination. Where is my speed?
    Thanks again for all of your information. I'm sure the PMDX-126 board will work flawlessly. This is the 3rd BOB I've had in the system. All were upgrades but this is getting expensive!
    Are there any hobby priced servo drives that have a self tuning feature?
    Best and thanks.
    Bill
    billyjack
    Apr 2005
    With the information presented above (I don't want to bore anyone with repeating it), can anyone give me an idea what speed I should expect out of this setup assuming ideal mechanical conditions?
    Bill
    billyjack
    Feb 2007
    canada
    Hi
    What encoders are you running ?
    If your interested, I can sell you 3 Viper 95 drives (@125 each) and If your not happy, i will give you your full money back including shipping.
    I'm sure they will solve your frustration. But i recommend differential encoders
    Larry K
    Larken Automation
    Manufacturer of CNC routers and Viper Servo Drives
    www.LarkenCNC.com and www.Viperservo.com
    Feb 2007
    canada
    Oops !!
    That was supposed to be a private message.
    Apr 2005
    Thanks for the reply Larry! I kind of thought your response was PM material but I sure do appreciate it anyway. I think I have found a solution to my issue (again, I think). The values I was using in Mach may have been very wrong for what I was trying to accompllish.
    Thanks for all the help guys.
    Bill
    billyjack
    Gold Member
    Mar 2003
    You are grossly miss-geared which makes your application very short on torque. 70 IPM is 350 RPM on the screw yet your motor can turn I'm guessing 3,500 RPM so you are using only 10% of the motor's available speed. If you geared the motor down 3:1, you'd need only 1/3 the torque from your motor and you'd reach much much higher speeds.
    Think of a manual transmission sports car when the light turns green. Do you want to be in 1st gear or 5th gear? It's the same engine and horsepower in either gear but 1st gets you a more spectacular getaway than 5th does. The engine has low torque compared to what the wheels need but it has a 7,000 RPM red-line and the wheels would tear off your car at 7,000 RPM if it were on jacks. You trade in excess RPM for torque using a transmission between the engine and wheels. You wouldn't build a car with its engine coupled 1:1 to wheels yet that's what you have when you couple a servomotor 1:1 to the screw.
    Mariss
    Apr 2005
    Thanks for chiming in Mariss. As always, your input is valued and appreciated.
    I guess I was under the assumption that the torque curve was highest at the low rpm of the servos. If that is a misconception on my part then what you say makes good sense.
    I''ve ordered a different pulley set from mcmaster to get the 3 to 1 ratio which is the best I can do with my current mounts.
    This is in no way meant to be criticism of Geckos!!!! I've used gecko's for years and really like them. I've just been kind of frustrated with this particular machine is not working as I expected.
    Many thanks guys!
    Bill
    billyjack
    Gold Member
    Mar 2003
    Servomotors have a continuous rated torque. This rating is the maximum torque load you may continuously apply to the motor without overheating it.
    This limit is independent of speed, which means it's the same limit at 1 RPM or 6,000 RPM. Power is torque times RPM; the motor produces it's rated power when it's turning at its rated RPM (typically 80% of its no-load speed).
    To get the rated power from the motor, the gearing must be such that the motor is turning at 80% of its no-load speed when your mechanism is moving at its maximum design speed.
    You won't get optimal gearing with a 3:1 reduction but you will be much better off than you were at 1:1 gearing. The geared output will have 3 times the torque you had at 1:1 reduction. The reflected moment of inertia will be reduced 9-fold and the motor will be able to accelerate the load much better to the speed you want.
    Mariss
    Mar 2012
    Guatemala
    Hi, good morning. I'm trying to use the gekodrive g320x I follow all the steps and all ok but in the step of connecting the servo motor I get the fault led. The fault led didn't go away for a while, then the fault led goes away I repeat all the steps and in the same step I get the fault led. I think is the current limit but my question is how to remove the fault led to try again
    1. Q: Breakout board for 320s?
      By Deviant in forum Gecko Drives
      Last Post: 12-22-2010, 06:44 AM
    2. Gecko 320s & Charge Pump
      By Mike F in forum Gecko Drives
      Last Post: 12-12-2006, 08:40 AM
    3. Q-Cad Cam Expert
      By Kevin Moore in forum General CAM Discussion
      Last Post: 11-09-2006, 12:05 AM
    4. CAM Expert
      By Jan in forum General CAM Discussion
      Last Post: 12-21-2003, 03:54 PM