    120volt 50 Hz mains input

    I noticed that the sellers of toroidal transformer power supplies show their output based on 120 volt 60Hz input, what happens to the power supply output voltage when the input voltage is 120volt 50Hz as I have here in Barbados.

    http://www.kelinginc.net/KL-5020.pdf

    The above power supply shows

    input 120Vac 60 Hz gives output of 51 volts DC output

    input 120Vac 50 Hz gives output of __? volts DC ouput

    I do not want to smoke the G540 when I order it.

    Jason
    Last edited by Jason Marsha; 03-28-2010 at 01:11 PM.


  2. #2
    Gold Member
    Join Date
    Mar 2003
    Location
    United States
    Posts
    2,782
    Downloads
    0
    Uploads
    0
    It will have the same voltage. The mains frequency doesn't affect the voltage.

    Mariss


  3. #3
    Registered
    Join Date
    Dec 2004
    Location
    Barbados
    Posts
    1,184
    Downloads
    0
    Uploads
    0
    Thanks Mariss.

    The reason I had originally asked is that I had seen some info on the web about a lower input frequency increasing the flux density and thought this would lead to a higher than stated output voltage.

    Jason


  4. #4
    Registered
    Join Date
    Dec 2008
    Location
    canada
    Posts
    226
    Downloads
    0
    Uploads
    0
    A transformer may have the same output voltage but will not have the same output capability... A lower frequency has a negative effect on the output power available... this is why high frequency switching power supplies only need a very small transformer...


    From http://www.smeter.net/daily-facts/4/fact15.php

    50 Hz vs. 60 Hz Power Transformers
    April 15th Fact-of-the-Day

    More iron and/or more turns of wire are required to have the same transformer winding inductive reactance at a lower frequency. Iron-core and copper-wire both cost money and take physical space, so transformer designers generally use no more of either than necessary to keep power losses reasonable at an intended operating frequency. As a result, power transformers designed for use in U.S. 60 Hz applications typically run very hot, and sometimes extremely hot, if used in countries that have 50 Hz power mains, even if they have windings to accommodate the higher voltages that also are used in most 50 Hz countries. Long-time U.S. suppliers to Europe and other parts of world with 50 Hz power know better, but U.S. companies that are just starting to offer their products internationally very often have major problems with power transformer overheating. ©2005 Tigertek, Inc. All rights reserved.


    From http://www.toroid.com/custom_transfo...bulletin_2.htm

    A 60Hz transformer has 20% higher rated power than a 50Hz transformer of the same size and weight.



    I'm just adding that I don't know exactly what the lower Frequency will do over all, but I think you should probably expect the voltage to drop off a little faster than the amperage ratings in the PDF and expect less available current overall.
    Last edited by Pandinus; 04-04-2010 at 09:25 AM. Reason: Added on


  • #5
    Gold Member
    Join Date
    Mar 2003
    Location
    United States
    Posts
    2,782
    Downloads
    0
    Uploads
    0
    You are correct, everything being equal a 50Hz transformer has to have 20% more iron than a 60Hz transformer for the same VA rating. That said, most transformers are 50Hz/60Hz rated. The main difference is the magnetizing current in the primary will be a little higher at 50Hz and the transformer will be a little warmer.

    Mariss


  • Similar Threads

    1. Replies: 2
      Last Post: 11-16-2011, 11:25 PM
    2. Using USA 110V Equipment on Euro 220V Mains!
      By diarmaid in forum General Electronics Discussion
      Replies: 120
      Last Post: 01-18-2010, 03:49 PM
    3. Mains Noise
      By Mooser in forum Gecko Drives
      Replies: 4
      Last Post: 10-15-2009, 09:46 PM
    4. Build Thread- Suggestions on New VSD-Core Based Mains Powered Drive
      By Adamj12b in forum Granite Devices
      Replies: 4
      Last Post: 05-05-2009, 03:28 PM
    5. Mains power stepper driver design
      By Balderscape in forum Stepper Motors and Drives
      Replies: 1
      Last Post: 02-21-2008, 10:54 AM

    Posting Permissions


     


    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.