From what i can see on page 24 of the manual is this.
X++ 17
X- - 15
X Home 17
Y++ 15
Y- - 18
Y Home 18
Z++ 19
Z- - 15
Z Home 19
But its really up to you how you want to do it. Inputs 17,18,& 19 are designated as the limit input for axes X,Y and Z respectively. Whether you use it for the -- or ++ or both is up to you.
If you don't want to use the Z-- then just disable it (click the tick in the Enable column to make it a cross)
The inputs are kept high (5V) internally, so yes, connect the LIM or other inputs to GND via a NC switch. Make sure you have the inputs set to active low (green tick in active low column).
Hope this makes sense