What is Ampacity...
Results 1 to 4 of 4
Thread: What is Ampacity...
    Registered ToyMaker's Avatar
    May 2003
    Default What is Ampacity...
    or, what size wire do I need to use when wiring my machine?
    Load Carrying Capacities or ampacities
    In part from Reference Data for Engineers: Radio, Electronics, Computer and Communications 7th Ed
    Max ambient 60C
    Code:
        CU Max      CU Max
    AWG   Dia Inch    Cir Mil  Dia cm   Area         lb    ohms     Ohms        free-air    enclosed
                                        Inch^2       /kft  /kft     /km         Amps        Amps
    32    0.008        63.2     0.020   4.964E-05    0.19  199.587  654.613     0.53        0.32
    30    0.010       100.5     0.025   7.894E-05    0.30  125.521  411.690     0.86        0.52
    28    0.013       159.8     0.032   1.255E-04    0.48   78.941  258.915     1.4         0.83
    26    0.016       254.1     0.040   1.996E-04    0.77   49.647  162.833     2.2         1.3
    24    0.020       404.0     0.051   3.173E-04    1.22   31.223  102.407     3.5         2.1
    22    0.025       642.4     0.064   5.046E-04    1.94   19.636   64.404     7.0         5.0
    20    0.032     1,021.5     0.081   8.023E-04    3.09   12.349   40.504    11.0         7.5
    18    0.040     1,624.3     0.102   1.276E-03    4.92    7.767   25.473    16          10
    16    0.051     2,582.7     0.129   2.028E-03    7.82    4.884   16.020    22          13
    14    0.064     4,106.7     0.163   3.225E-03    12.43   3.072   10.075    32          17
    12    0.081     6,529.9     0.205   5.129E-03    19.77   1.932   6.336     41          23
    10    0.102    10,383.0     0.259   8.155E-03    31.43   1.215   3.985     55          33
    8     0.128    16,509.7     0.326   1.297E-02    49.98   0.764   2.506     73          46
    6     0.162    26,251.4     0.412   2.062E-02    79.46   0.481   1.576    101          60
    4     0.204    41,741.3     0.519   3.278E-02   126.35   0.302   0.991    135          80
    2     0.258    66,371.3     0.654   5.213E-02   200.91   0.190   0.623    181         100
    1     0.289    83,692.7     0.735   6.573E-02   253.34   0.151   0.494    211         125
    0     0.325   105,534.5     0.825   8.289E-02   319.46   0.120   0.392    245         150
    00    0.365   133,076.5     0.927   1.045E-01   402.83   0.095   0.311    283         175
    000   0.410   167,806.4     1.040   1.318E-01   507.96   0.075   0.247    328         200
    0000  0.460   211,600.0     1.168   1.662E-01   640.53   0.060   0.196    380         225
    Robotic regards,
    Tom
    "Words of war put all men in pieces; a war of words puts peace in all men."
    - - Ross Mackenzie
    Dec 2003
    Ampacity is another way of saying current capacity, this can vary for for a given conductor apart from the gauge, it can also depend on where it is used and the nature of the insulation etc.
    This is an exerpt from the Wiring of Industrial machines NFPA.
    You will need to calculate or obtain the expected current draw of your circuit and use the chart.
    Often, a larger gauge is used for where a higher durability requirement is needed, as in Flex chain carriers etc.
    Attached Thumbnails Attached Thumbnails What is Ampacity...-ampacity-pdf
    Oct 2005
    the Netherlands
    If some1 did not completely understand how to use this.
    Would you advise to overkill and use way heavy/thick wiring or should one really research his HW to determine whats right for him.
    I don't mind researching but also i wouldn't mind finishing my research.
    if i'm right this has to do with how much current a wire can transport before burning up.The more current to be transported the more mass you'll need to get it across without burning the medium(copper).thats why overkill seemed the best option to me.
    THX in advance
    Finally CHIPS you can have as much as you can without the doc. complainting about your cholesterol.
    Nov 2006
    ironDigit
    this link might help
    http://www.csgnetwork.com/voltagedropcalc.html
    It is a nice calculator. If you play with it you can see the effects of different conductors on voltage drop. Voltage drop is bad. Voltage drop is caused by the resistance in the wire. See the tables above.
    The power is lost as wattage (volts drop*amps). If you have lots of voltage drop from resistance and distance you are turning the wire into a heater - this is bad. The table and pdf above show you the values to plug into formulas or use can use this calculator.
    Use the right size wire and you don't have a heater that might create a fire. You also don't pay for electricity that you aren't using. Don't go too big on the wire or you will pay a ton of money for the wire.
    maybe this helps
What is Ampacity...
What is Ampacity...