Faulty Z+ Hardware. Over travel switch, wiring or I/O
Good Day Frieds & Expert.
appreciate all help & advice. I have problem with fanuc 15T system with "OT007 z+ overtravel (Hard) alarm" and cannot be RESET.
Did check all wire and overtravel switch working find. Did manually force the switch and check at PCDIagnosis bit did change 1 to 0 (on & off) X39.2 DI.
It somethin like "internal force signal" which cause this issue. It's related to Parameter seeting?? Which parameter it's & how to resolve this problem.
DID TRY "caN + P" aLSO NOT WORKING.
anybody knOW how to internally disable / reset this alarm.
is there any link to between Parameter 1000, Parameter 1005 & Parameter 1815.
What is the correct setting for those Parameter?
I really need urgently support since this Danichi 152 was sleep almost 3month.
anybody can help much more appreciate.
thx
Faulty Z+ Hardware. Over travel switch, wiring or I/O
***********************************************************
*~~Darwinian Man, though well-behaved, At best is only a monkey shaved!~~*
***********************************************************
*__________If you feel inclined to pay for the support you receive__________*
*_______Please give to charity http://www.oxfam.org/en/getinvolved_______*
***********************************************************
DEAR FRIEND ,
PLEASE CHECK THE LIMIT SWITCH OF THE OTHER END [OT 007 +OVERTRAVEL (HARD) THE STROKE LIMIT SWITCH LOCATED AT THE POSITIVE SIDE WAS TURNED ON].I MEAN + SIDE OF AXIS, Also cable and 24 v supply on other side Limit sw.
HOPE YOU CAN RUN THE MACHINE NOW.
REGARDS
PRABHAT MISHRA
prabhatmishra@gmx.com
Al the man,
I posted this message for update review not for JlpD so please do not mind as you are so intelligent so better to talk in a technical way.
Regards and honor to your presence and interactivity
Prabhat