    Default Kel-Vista UR 175/1000 - "INV. LOW VOLT DC LINK"

    Kellenberger Kel-Vista UR 175/1000 CNC Grinder with a GE Fanuc Series 2li-T control

    1180 PROX. SWITCH SPEED T1/T2 FAULTY
    435 X AXIS: INV. LOW VOLT DC LINK
    435 Z AXIS: INV. LOW VOLT DC LINK
    435 C AXIS: INV. LOW VOLT DC LINK

    I have 480 volts going to the cabinet. 480 volts going to the power supply. The middle Fanuc PLC(?) shows 5, but the one on either side has "-". And the Danfoss has no power going to it. No breakers are tripped.

    Any suggestions?

    https://goo.gl/photos/Hd4fsHEy1hm39ga18

    Similar Threads:


  2. #2
    Registered
    Join Date
    Feb 2015
    Posts
    161
    Downloads
    0
    Uploads
    0

    Default Re: Kel-Vista UR 175/1000 - "INV. LOW VOLT DC LINK"

    If this happens at power on, it could be the unit with the "5" on the LED.(That unit is a servo amplifier.) Could be an issue with the servo amplifier of the power supply module next to it.



  3. #3
    Registered
    Join Date
    Feb 2014
    Location
    United States
    Posts
    11
    Downloads
    0
    Uploads
    0

    Default Re: Kel-Vista UR 175/1000 - "INV. LOW VOLT DC LINK"

    I have a Hardinge tech showing up today, hopefully.

    And hopefully he'll be able to show me a few things also. Best case scenario - he'll prove I'm an idiot and it'll be something easy. Worst case scenario, he'll be here for a full day or 2.



  4. #4
    Registered
    Join Date
    Apr 2017
    Location
    United States
    Posts
    28
    Downloads
    0
    Uploads
    0

    Default Re: Kel-Vista UR 175/1000 - "INV. LOW VOLT DC LINK"

    Is the 5 on the power supply unit, it is the unit first in the line Fanuc units, Psu-spindle amp-servo amps. The power supply unit has a fuse inside behind the bus bar. With the power off, wait for the led in the unit to extinguish, this is the bus voltage (300vdc or 600vdc), then open the power supply top cover, should be gray, the bus bars need to be removed from it so not connected to the spindle amp. With a DVM check across the bus + to - should be shorted, if open, your psu unit is bad.



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Kel-Vista UR 175/1000 - "INV. LOW VOLT DC LINK"

Kel-Vista UR 175/1000 - "INV. LOW VOLT DC LINK"