Need Help!- 1000 sequence alarm
Member
Last edited by =aike=; 04-26-2017 at 04:46 AM .
Registered
Re: 1000 sequence alarm
Check A bits in status in PMC. Trace in ladder.
Member
Re: 1000 sequence alarm
Please more detailed from this part. Where is A bits?
I can see the status. But don't see any bits. What to do?
Registered
Re: 1000 sequence alarm
A bits are alarm bits on PMC side. If any are on, then trace in ladder to find why it is on. Or consult MTB. I believe alarms in the 1000 range are MTB alarms, not FANUC alarms.
Member
Re: 1000 sequence alarm
The problem was solved.
http://www.cnczone.com/forums/fanuc/...e-blocked.html
Unblock pallet clamp/unclamp sendor, setting pallet parameters.
Need Help!- 1000 sequence alarm