Fanuc spindle drive

Last week I was doing a chucking job on a mori seiki sl15 with a fanuc 10tf control. Almost through with the job. Put a part in, closed the collet, and pushed the cycle start button....nothing. couldn't get an alarm number on the crt at all. I opened the cabinet and there it was, the dreaded AL-12. I sent the fanuc spindle drive to a repair facility to have it gone over. I got it back on Thursday (quick service) and installed it yesterday. Double & triple checked the wiring to make sure it was correct. I flipped the breakers on the main panel, then flipped the power switch on the end of the machine. The hydraulic pump and cooling fans came on, then I pushed the start buton on the control.....good so far. When I released the e-stop button, the machine shut down and tripped the 50A breakers in the main panel. I pushed the
e-stop, turned the machine off and reset the breakers. When I turned
the main switch back on I get AL-4 (fuse blown).
Any thoughts what might have caused this?

Thanks,
Martin

Last edited by mrwhittle; 07-29-2006 at 01:01 PM.
Reply With Quote

  #2  
Old 07-29-2006, 01:08 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,538
Al_The_Man is on a distinguished road
Buy me a Beer?

Hopfully the repair facility replaced the Firing board as well as the IGBT's
And did a complete test on it.
The only other issued is if the motor itself has a problem? Hopefully the fuses went before the drive blew again.
I would replace the fuses and disconnect the motor completely from the drive and power up, if the fuse blows or you get an AL-12, it is most likely the drive again.
If they hang in there with no alarm, check the motor.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 07-29-2006, 01:49 PM
 
Join Date: Mar 2005
Location: US
Posts: 27
mrwhittle is on a distinguished road

Thanks for the quick reply Al The Man!

I'm not sure what all they did, but they said they replaced all the transistor modules.

I don't have a local source for the fuses, if you're talking about the large screw on fuses. I will order those.

Can I tell anything about the motor with an multi-meter? Also is the spindle motor a standard 3 phase motor that could be wired directly to a 240V 3ph breaker to see if it will run that way, or is that a good way to scortch something?

Thanks again,
Martin
Reply With Quote

  #4  
Old 07-29-2006, 03:03 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,538
Al_The_Man is on a distinguished road
Buy me a Beer?

An ordinary meter will not tell you alot, the best way is to borrow/use a megger, this is a high voltage insulation tester that many electricians will have access to. This will detect if there is a ground on any of the motor phases, If it is not a P.M. 3ph motor (which IIRC it is not) . then it is just a vector drive rated motor so should be possible to hook up to the right 3 ph voltage and test it that way with a clamp on ampmeter and test each phase for balance.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 07-29-2006, 07:09 PM
 
Join Date: Mar 2005
Location: US
Posts: 27
mrwhittle is on a distinguished road

I'll ask my electrician neighbor if he has one or knows where I can get my hands on one. If not, I might have to wire the motor direct and see if any sparks fly. The motor looks like maybe 15 or 20hp, I'll check it. Do you think 30a fuses will start it with no load?

I sure appreciate your help, Al.
Thanks,
Martin
Reply With Quote

Sponsored Links
  #6  
Old 07-29-2006, 07:13 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,538
Al_The_Man is on a distinguished road
Buy me a Beer?

On 240 if time delay fuse they should hold in ok.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #7   Ban this user!
Old 07-29-2006, 08:14 PM
 
Join Date: Dec 2005
Location: USA
Posts: 3,319
NC Cams is on a distinguished road

The velocity drive on my Fanu 5T will pop the fuses INSTANTANEOUSLY if the 3 phase is wired out of phase.

Simply switch any 2 wires of the 3 phase input, problem solved.

Dunno if that will work here but stranger things could happen.
Reply With Quote

  #8   Ban this user!
Old 07-29-2006, 10:53 PM
 
Join Date: Jul 2006
Location: usa
Posts: 40
Arrow Control is on a distinguished road

On Fanuc AC drives phasing doesn't matter, I've always been leary of line starting FANUC spindle motors - not sure if they are rated for that inrush. If you do try a megger make sure you disconnect the wires from the drive.....
Reply With Quote

  #9   Ban this user!
Old 07-30-2006, 04:20 PM
 
Join Date: Mar 2005
Location: US
Posts: 27
mrwhittle is on a distinguished road

Thanks for the input!

If I can't borrow a megger, would a cheapie like this do the job?

http://www.grainger.com/Grainger/wwg...mId=1613559264

Thanks,
Martin
Reply With Quote

  #10  
Old 07-30-2006, 04:42 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,538
Al_The_Man is on a distinguished road
Buy me a Beer?

Not really, that is just an ordinary VOM, a megger impresses a high voltage across the circuit being measured, and test if a ground exists at high voltage that may not show up with the couple of volts you have on a VOM.
Another simple way is to use a 120vac circuit, make sure the motor has a ground connection on it to system ground.
Using a 100watt lamp holder with one side connected to 120vac (a hot on an outlet) and the other lamp lead touch to one of the phases, if you get a light it show there is a ground on the motor.
The motor should be vector drive rated which is a higher standard than the regular motor so I don't see any harm running it on 3ph as long as the voltage is correct.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 07-30-2006, 05:23 PM
 
Join Date: Mar 2005
Location: US
Posts: 27
mrwhittle is on a distinguished road

Now you're getting down to my technology level!!

I'll let you know what happens tomorrow.

Thanks again,
Martin
Reply With Quote

  #12   Ban this user!
Old 07-30-2006, 06:31 PM
 
Join Date: Dec 2005
Location: USA
Posts: 3,319
NC Cams is on a distinguished road

And if you do the lamp bulb trick incorrectly, you could electrocute yourself or someone else. The technique Al used should not be tried by just ANYONE!!!

For example, if you inadvertently catch the ground side of the AC line, you'll get a totally different experience/result than if you touch the "hot" side. Some circuits MAY be wired wrong so don't trust the wire color code - my business partner's shop had some real silly, half fast wiring in it.

"Code? I don't have a code, just some hayfeber" pretty much described his building's wiring...

Experience is needed to prevent some real ugly experiences when you try to do psuedo meggar tests.

Contact a local motor shop. Ask to rent or borrow their meggar. Better yet, plan on paying a service call to have their technician do the meggar test. Doesn't take more than half hour to do the test. Besides, if you can't tell the difference between a VOM and a meggar, outside help may be in order.

Whatever the motor shop charges, it WILL be cheaper than a hospital bill. If the motor is fried (shorted arm or field, they might do the test for free if you have them do the motor repair job.

Cost me $175 to have one pole of a field coil redone and re-varnishe along with meggar check of a unobtainable pancake motor on a Excello mill. I R&R'd and reassebled the motor, they did the arm and field coil check/repair.

Replace bearings while I was at it and had motor armature rebalanced for good measure. The thing is now good for another 25 years of service...
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On





All times are GMT -5. The time now is 01:27 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361