    Question Fanuc OM

    I would like to know how to send Macro files(O9000-O9999)into controler. Which parameter must be change to allow transmition? Thanks majstr


  2. #2
    Registered
    Join Date
    Nov 2005
    Location
    USA
    Posts
    274
    Downloads
    0
    Uploads
    0
    Quote Originally Posted by majstr
    I would like to know how to send Macro files(O9000-O9999)into controler. Which parameter must be change to allow transmition? Thanks majstr

    Check P# 3202 See if it has NE8 and NE9, Now I am not sure of this goes for an OM or not but FANUCs do not change a whole lot as far as that one. It is the same on a 6 all the way to 21. If you show these then you need to turn them off (from 1 to 0) Be sure and turn PWE on first to change them.

    Bluesman


  3. #3
    Registered
    Join Date
    Mar 2006
    Location
    Thailand
    Posts
    1
    Downloads
    0
    Uploads
    0

    Fanuc Om

    Help me, How to repair cnc Fanuc OM This machine cannot change tool He Show Error code P/S alarm 099. And Input Output data not work also
    Thank you...


  4. #4
    Registered
    Join Date
    Jan 2006
    Location
    usa
    Posts
    26
    Downloads
    0
    Uploads
    0
    Set parameter 389.2 to 0 for 8000 programs, and parameter 10.4 to
    0 for 9000 programs. This allows output or editing of these ranges.
    You should be able to upload (computer to cnc) 9000 prgm without
    the parameter set. Must be in edit mode with data protect key turned
    to off.