Old 04-05-2011, 10:24 PM
qmas99 is on a distinguished road
TLO macro
O9010(TOOL CHANGE)
G0G91G30Z0
G91G30X0Y0
#100=#100+1
DO1
M6T#100
G90G53X15.Y-2.8
#3006=1(TAKE TLO ON 3IN BLOCK)
G10L10P#100R#5023
#100=#100+1
END1
M99
I have tool change macro above, set to G100, question:
Instead of setting #100=1 or set #100 manually every time I run G100, I want to run G100 T10, is there any system variable that can get #10 to put in #100.
Old 04-06-2011, 12:56 AM
angelw is on a distinguished road
Originally Posted by qmas99 View Post
O9010(TOOL CHANGE)
G0G91G30Z0
G91G30X0Y0
#100=#100+1
DO1
M6T#100
G90G53X15.Y-2.8
G10L10P#100R#5023
#100=#100+1
END1
M99
I'm not quite sure what you want to do exactly, except that you're setting the TLO with the Macro program. I'm not sure why you increment #100 by 1 at the start of the program and in the DO1 routine. Are you calling O9010 repeatedly from your main program? There is no Conditional statement associated with the DO1 routine, accordingly, there is no need for it.
If you only need to load a tool number into #100 and therefore access the corresponding offset for that tool, the T parameter will be passed to #20 in the Macro program.
O9010(TOOL CHANGE)
G0G91G30Z0
G91G30X0Y0
#100=#20
DO1
M6T#100
G90G53X15.Y-2.8
G10L10P#100R#5023
#100=#100+1 (Not sure why you increment #100 here)
END1
M99
Alternatively, System variable #4120 is the Modal information for T.
Regards,
Bill
Old 04-06-2011, 06:40 AM
christinandavid's Avatar
christinandavid is on a distinguished road
Looks like he uses this loop to quickly set his tool lengths before he starts running.
Now he wants to start it from a specific tool.
To reiterate what angelw said :-
Replace that
#100=#100+1.
(at the start)
with: -
#100=#4120 (saves current spindle tool)
IF[#20NE#0]THEN #100=#20 (overwrites it with the T# if you specified it)
If you want this loop to repeat (when setting up, for example), alter to a WHILE[ ] DO command so that it will repeat forever (until RESET anyway)
Then, if you only want a mid-batch 'one shot' tool length check (ie when you specify a T), at the end of your loop, put something like: -
IF[#20NE#0]GOTO10 (jumps out of loop if you specified T)
#100=#100+1.
END1
N10 M99
DP
Old 04-06-2011, 02:26 PM
O9010(TOOL CHANGE)
G0G91G30Z0
G91G30X0Y0
#100=#20
DO1
M6T#100
G90G53X15.Y-2.8
G10L10P#100R#5023
END1
M99
Regards,
Bill
Thanks Bill,
yes #100=#20 does the trick, works with G100T#
I want to use it in MDI to do TLO, that is why #100+1
Old 04-06-2011, 05:15 PM
Thanks Bill,
That still doesn't explain why the #100+1. The current structure of your DO Loop will only run the one time because there is no conditional statement for it to do else-wise. If you included a WHILE[] conditional statement as suggested by Kiwi, then the loop would repeat as long as the WHILE[] statement tested true. For example, you could specify a range in your G100 call and the DO loop would repeat while #100 was less than, or equal to the upper limit of the range.
G100 T? U?
#100=#20
IF[#21EQ#0]THEN #21=#100 (if the upper range is not specified, set it to the lower range so the loop only sets the one tool)
WHILE[#100 LE #21] DO1
#100 = #100 + 1
END1
Regards,
Bill
Old 04-06-2011, 06:36 PM
When DOm is specified without specifying the WHILE statement, an infinite loop ranging from DO to END is produced. (got from the operator's manual). #100+1 keep adding up untill I hit RESET.
QM
Old 04-06-2011, 07:12 PM
QM
You're so right. I've never used a DO loop with out some condition, just for the reason of good structure and controlling the Loop.
Because you have the tool change inside the DO loop, don't you get an alarm if #100 exceeds the maximum number of tools available in the magazine? If yes, then your method would rely on the operator to be aware and abort using Reset before that occurs, as opposed to controlling if either 1, or to a maximum tool number should be set.
Regards,
Bill
DO1
M6T#100
G90G53X15.Y-2.8
G10L10P#100R#5023
#100=#100+1
END1
M99
Old 04-06-2011, 08:38 PM
You learn something new everyday (I always used to put WHILE[#0EQ#0]...).
I think the message to the operator when you exceed the maximum tool should be . . . (WHY DONT YOU GO AND DO1...)
DP
Old 04-07-2011, 03:00 AM
sinha_nsit is on a distinguished road
An isolated DO1, without a matching WHILE statement, should give syntax error.
If a subprogram (O9000) is called by a T-code, the value specified with T automatically gets stored in #149, for use inside the subprogram.
Old 04-07-2011, 04:00 AM
Hi Sinha,
QM is correct with regards to the DO statement. This was new to me, as I've always used a conditional statement to control the loop. Following is a direct cut and paste from the Fanuc manual.
When DO m is specified without specifying the WHILE statement, an
Regards,
Bill
  #11   Ban this user!
Old 04-07-2011, 04:16 AM
Right.
Actually, isolated END 1 is not permitted, IIRC. There was a mix up.
need help wana make macro for getting tool change by giving tool pot no on vmc instea ghevari Parametric Programing 0 02-14-2010 12:26 PM
Need Help!- M6 tool change macro at6c Mach Mill 0 08-08-2009 07:41 AM
Help for tool change macro on OM VMC Namnp2007 Fanuc 3 08-12-2008 11:18 AM
Tool Change Macro cncdiag Mazak, Mitsubishi, Mazatrol 0 03-26-2007 02:20 PM
A sample tool change macro. gar Haas Mills 17 08-22-2005 05:13 PM