    Fanuc O-T control

    HELLO! I NEED HELP!!!
    WE HAVE A JOHNFORD MACHINE WITH FANUC OT CONTROL, DRIVES SERIE ALPHA, WHEN WE START THE MACHINE SUDDENLY APPEARS ALARM 19 ON THE SPINDLE AMPLIFIER, AFTER THAT APPEARS THE ALARM 401 MACHINE NOT READY, SOMEONE KNOWS WHAT HAPPEN IT!!!


  2. #2
    Registered resuengineering's Avatar
    Join Date
    Nov 2007
    Location
    Netherlands
    Posts
    63
    Downloads
    0
    Uploads
    0
    Alarm 19 on Spindle driver means

    Phase U current detector circuit excessive offset

    Meaning,

    The offset voltage for the phase U current detection circuit is too high,
    this check is made after power on the machine.

    Cause:

    Loose contact of the PCB board - check connections

    phase current detection defective. - replace PCB

    A/D converter defective - Replace PCB

    Also check the input power on the PSM module


  3. #3
    Registered
    Join Date
    Jun 2009
    Location
    Mexico
    Posts
    93
    Downloads
    0
    Uploads
    0

    Power not on

    Thanks, but the power is not on, the main contactor not on, the alarm apeears 2 seconds, after that appears on the displays [-] but the power never goes on.


  4. #4
    Registered resuengineering's Avatar
    Join Date
    Nov 2007
    Location
    Netherlands
    Posts
    63
    Downloads
    0
    Uploads
    0
    these checks are performed, when supplying power to PSM module
    this has a seperate control bus power supply, no need to charge the DC Bus for this alarm

    all phases are excisting??


    you say no power, but no power means no display start up also!!!


  • #5
    Registered
    Join Date
    Jun 2009
    Location
    Mexico
    Posts
    93
    Downloads
    0
    Uploads
    0

    Question Alarm 401 OT control FANUC

    To be clear:

    1.- Put on breaker 460 VAC
    2.- on the display from Spindle Amplifier appears suddenly alarm 19, after that appears --
    3.- On the screen appears NOT READY
    4.- When I push the button OT Release appears Alarm 401
    5.- MCC never go on
    6.- on the display from PMS, and drives appears -- only


  • Similar Threads

    1. Help with Fanuc 6m control
      By inaman in forum Fanuc
      Replies: 5
      Last Post: 02-03-2012, 01:49 PM
    2. Need Help!- Velocity Control Drives and Fanuc 2000C control
      By redialtone in forum Fanuc
      Replies: 3
      Last Post: 06-21-2010, 10:26 PM
    3. Fanuc O-T control
      By Antonio Arguijo in forum Fanuc
      Replies: 7
      Last Post: 06-20-2010, 05:46 PM
    4. FANUC OM CONTROL
      By gabedrummin in forum Fanuc
      Replies: 0
      Last Post: 08-28-2008, 05:41 PM
    5. FANUC OT control need dnc help
      By mike10 in forum Fanuc
      Replies: 5
      Last Post: 10-17-2006, 04:27 PM

    Posting Permissions


     


    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.