    Exclamation Problem with RS232 connection through long cable??!!

    We have a VMC20 and can only get the machine to DNC feed if the computer is sitting with a 4ft (or so) cable connecting them. We have built a new office area and want to have the computer about 30 feet away? Whats the problem??!


  2. #2
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,933
    Downloads
    0
    Uploads
    0
    I have used RS232 in the past with runs longer than 30ft with no problem.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  3. #3
    Registered
    Join Date
    May 2004
    Location
    United States
    Posts
    4,519
    Downloads
    0
    Uploads
    0
    Have you tried a different PC. Maybe something is wrong with your port. Another issue I have seen on longer cable runs is you have to slow the baud rate down at the machine and at the PC. I think for most machines 100' is the longest recommended. I have run over 150' before by slowing the baud rate down.
    http://www.kirkcon.com/


  4. #4
    Registered
    Join Date
    Feb 2009
    Location
    usa
    Posts
    4,000
    Downloads
    0
    Uploads
    0
    And make sure the cable is not strung over the shop lights. I have run over 100ft no problem.


  • #5
    Registered Neal's Avatar
    Join Date
    Mar 2003
    Location
    Chatsworth, Ca
    Posts
    900
    Downloads
    0
    Uploads
    0
    You can DNC up 100 ft with no issue IF you have no noises being injected into the cable. Can you transfer files to and from the machine from the new location? If you can than either you have a low signal voltage (doubtful) or the routing of you cable is causing signal distortion. Keep away from ANY source of RF, I.E. flouresent lights, EDM, high power lines, enen those inside the walls.

    Neal


  • Similar Threads

    1. RS232 connection
      By mamehdi2000 in forum DynaCNC
      Replies: 1
      Last Post: 10-03-2011, 07:16 PM
    2. Replies: 9
      Last Post: 03-10-2011, 03:25 PM
    3. RS232 connection
      By ramsey321 in forum Tree
      Replies: 2
      Last Post: 02-05-2011, 03:15 PM
    4. Help with FANUC 18i-mb rs232 connection.
      By ulises3.14 in forum Fanuc
      Replies: 5
      Last Post: 02-23-2010, 01:07 PM
    5. USB to RS232 connection
      By stevo1 in forum Machine Problems, Solutions , Wireless DNC, serial port
      Replies: 32
      Last Post: 08-16-2008, 02:15 AM

    Posting Permissions


     


    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.