    On inverter setup i did by mislate change pd 04 to 01 after push SET button- fuse brake down!
    After replace fuse i did plug in power - and nothing-- for short tiime i saw smoke comming out!!
    Any idea what the hack is wrong!
    Thanks.
    Adi
    Gold Member
    Jan 2005
    Default Re: Huanyang inverter dead after set Pd004 to 01 by mistake!
    Quote Originally Posted by adi7791 View Post
    Hello Guys!
    Thanks.
    Adi
    What where you trying to run with it, need more information, any smoke is not a good sign
    Mactec54
    Nov 2017
    Slovenia
    Hi.
    is cnc router setup, runing 2,2 kw water cooled spindle- all was fine and smooth run- figured out how to connect with board to run from Mach 3
    just search for setup to start with 0hz- so i can raise revolutions in software- and when i change pd04 to 01 bum. fuse downt and now just lil smoke for short time when is connected to
    main power- figured out that pd04 is for main power frequeny-- here is 50 mhz-
    May 2012
    canada
    Hi.
    Are you sure that parameter is for main power frequency and not motor rated frequency? Normally you dont have to specify what the main frequency is, most VFDs wont care. And even if you did specify the wrong motor frequency it shouldn't damage the drive. It could just be a faulty drive. I looked into Huanyang drives a year or so ago and decided the savings was not worth the risk. Seemed like quality problems were not uncommon, manual and parameters were hard to read, and there were counterfeit drives copying the huanyang that were even more poorly built.
    You might have better luck asking on the VFD forum on practical machinist. The guys on there are great, helped me save a $2000 drive last year.
    Gold Member
    Jan 2005
    Hi.
    Here are the correct settings, you can not use these spindles with a 0Hz and PD04 can only be set at 400Hz, your 50Hz power frequency has very little to do with what you are running, you have a minimum speeds these spindles can run at, and for the water cooled it is 6,000 RPM =100Hz
    These are the minimum Parameters that have to be set, or you will over heat the spindle at low speed and damage the VFD and Spindle
    Huanyang Mactec54
    2.2Kw
    PD000=0 for Parameter unlock ( 1 ) for Parameter Lock
    PD001=0 (1 For Remote Control)
    PD002=0 ( 1 For 0-10v Terminal Control or Remote Trim Pot Control ) ( J1 Also Needs to be set for Terminal Control )
    PD003=400
    PD004=400
    PD005=400
    PD007=20
    PD008=220 (Motor Rated Voltage )
    PD009=15
    PD010=8
    PD011=120 ( 100 Minimum Setting with Quality VFD, 120 is Safe)
    PD13= 08 is for Factory reset, Only use this to set VFD to Factory Default Settings
    PD014 Acceleration=12 ( Adjust to suit)
    PD015 Deceleration=12 (Adjust to suit)
    ( PD15 is ignored IF PD26=1 Then the Spindle will Coast to a Stop)
    PD041=8 ( Carrier Frequency )
    PD141=220 ( Motor Rated Voltage )
    PD142= 9 ( Motor Amp Rating 2.2Kw Spindle 9 amp )
    PD143=2 ( Motor Number of Poles)
    PD144=3000 (Max Motor RPM) =3,000= (24,000)
    PD70=0 ( This may need to be set to 1 if Control Voltage is 0-5v )
    PD72=400
    PD73=120 ( 100 Minimum Setting )
    Mactec54
    Gold Member
    Jan 2005
    Quote Originally Posted by mmurray70 View Post
    Specifying any wrong parameters will damage any VFD Drive, some are a little more forgiving than others, when you are dealing with 400Hz and above spindles it all has to be set correct, or you will see the smoke
    The savings are well worth it, if the buyer gets the real Huanyang VFD Drive, they are very good and last just as well as any other VFD Drive, providing the correct parameters are set to match the motor's being used with them, some VFD Drives are more forgiving if someone does not use the correct parameters, but over time they will fail as well
    Mactec54
  7. #7
    May 2012
    canada
    How much do they cost nowdays? You can get an automation direct GS2 3hp for $309 and free shipping. Certainly appears to be built better. And you get a real manual clearly explaining every possible parameter to every detail, no worries about accidentally buying a counterfeit, you know you will actually get the KW rating you order, and if you happen to have a problem you have a real company to call for help/warranty. Seems like a better deal for me anyway, still a very cheap drive and potentially a lot less headaches for maybe $100 or so in the difference. If you shopped around you could probably find a brand name drive even cheaper then that too.
  8. #8
    Mar 2003
    About $135, for a "genuine" version. Cheaper for a noname knockoff.
    UCCNC 2017 Screenset
    http://www.thecncwoodworker.com/2017.html
    http://www.thecncwoodworker.com/2010.html
    http://www.g-forcecnc.com/jointcam.html