Need Help! Problem jig grinding machine. - Page 4
Page 4 of 5 FirstFirst 12345 LastLast
Results 37 to 48 of 55
Thread: Problem jig grinding machine.
  1. #37
    Gold Member TomKerekes's Avatar
    May 2006
    Default Re: Problem jig grinding machine.
    Hi vadim_cnc,
    Before running KMotionCNC please test and tune the Axis with the KMotion.exe Step Response Screen at various Velocities, Accelerations, and Jerks. Verify that your Axis is properly following the commanded trajectory. See:
    Dynomotion
    You should also determine the encoder resolution of your system. See:
    Dynomotion
    Each Axis has Max Limits on Error, Output, and Integrator. Your Max Output is set at 1000 (~5V). Increase to 2047 for a maximum of 10V Output. See:
    Dynomotion
    After you know your Resolution and Max Velocities and Accelerations that work well for your system set them in KMotionCNC | Tool Setup | Trajectory Planner Screen. See:
    Tool Setup Trajectory Planner
    HTH
    Regards
    TK
    http://dynomotion.com
  2. #38
    May 2006
    Hi vadim_cnc,
    I just noticed your C code has a factor of 3 included. It would be best (more logical) to remove that as any gain can be included in the Axis Parameters PID gains. Having that included would require you to limit the output to 1/3 of 2047 otherwise you might overflow the maximum allowed DAC value.
    Regards
    TK
  3. #39
    Nov 2016
    Hi, Tom!
    Now this axis works good, we tuned it.
    Now we trying to set up MPG like this:
    Problem jig grinding machine.-s-l1600-jpg
    We trying MPG examples in C programs folder, but nothing succeeded. Last tested is MPGServiceSmoothHardwareEnc. compiles good.
    For testing we changed axis to 4 (MPG connected as on picture)
    Problem jig grinding machine.-jpg
    Also we changed ENABLE_MPG, HANDWHEEL_EN, SELECT adn FACTOR bits to virtual.
    As well we can see what encoder works after connecting to Kanalog (see picture):
    Code:
    #include "KMotionDef.h"
    #define DIR_BIT0_POS 144
    #define DIR_BIT0_NEG 145
    #define MPG_INPUT_AXIS 4
    #define TAU 0.08 // smoothness factor (Low Pass Time constant seconds)
    #define FINAL_TIME 1.0 // Set final dest after this amount of time with no change
    #define ENABLE_MPG 1056
    #define SELECTX 1024
    #define SELECTY 1025
    #define SELECTZ 1026
    #define SELECTA 1027
    #define FACTOR1 1040
    #define FACTOR10 1041
    #define FACTOR100 1042
    #define FACTOR200 1043
    #define HANDWHEEL_EN    1056
    main()
        int BitA,Change1=0,Change2=0, DiffX2;
        int PosNoWrap, NewPos, Pos=0, wraps;
        double Factor=0;
        SetBit(152);
        SetBit(157);
        SetBit(158);
        ch0->InputMode=ENCODER_MODE;
        ch0->OutputMode=DAC_SERVO_MODE;
        ch0->Vel=100000;
        ch0->Accel=2e+006;
        ch0->Jerk=2e+006;
        ch0->P=1;
        ch0->I=0;
        ch0->D=0;
        ch0->FFAccel=0;
        ch0->FFVel=0;
        ch0->MaxI=200;
        ch0->MaxErr=40000;
        ch0->MaxOutput=2000;
        ch0->DeadBandGain=1;
        ch0->DeadBandRange=0;
        ch0->InputChan0=0;
        ch0->InputChan1=0;
        ch0->OutputChan0=0;
        ch0->OutputChan1=0;
        ch0->MasterAxis=-1;
        ch0->LimitSwitchOptions=0x100;
        ch0->LimitSwitchNegBit=0;
        ch0->LimitSwitchPosBit=0;
        ch0->SoftLimitPos=1e+009;
        ch0->SoftLimitNeg=-1e+009;
        ch0->InputGain0=1;
        ch0->InputGain1=1;
        ch0->InputOffset0=0;
        ch0->InputOffset1=0;
        ch0->OutputGain=1;
        ch0->OutputOffset=0;
        ch0->SlaveGain=1;
        ch0->BacklashMode=BACKLASH_OFF;
        ch0->BacklashAmount=0;
        ch0->BacklashRate=0;
        ch0->invDistPerCycle=0.00025;
        ch0->Lead=0;
        ch0->MaxFollowingError=10000000;
        ch0->StepperAmplitude=100;
        ch0->iir[0].B0=0.027497;
        ch0->iir[0].B1=0.027497;
        ch0->iir[0].B2=0.000000;
        ch0->iir[0].A1=0.945006;
        ch0->iir[0].A2=0.000000;
        ch0->iir[1].B0=1.000000;
        ch0->iir[1].B1=0.000000;
        ch0->iir[1].B2=0.000000;
        ch0->iir[1].A1=0.000000;
        ch0->iir[1].A2=0.000000;
        ch0->iir[2].B0=1.000000;
        ch0->iir[2].B1=0.000000;
        ch0->iir[2].B2=0.000000;
        ch0->iir[2].A1=0.000000;
        ch0->iir[2].A2=0.000000;
        ch1->InputMode=ENCODER_MODE;
        ch1->OutputMode=DAC_SERVO_MODE;
        ch1->Vel=100000;
        ch1->Accel=2e+006;
        ch1->Jerk=2e+006;
        ch1->P=1;
        ch1->I=0;
        ch1->D=0;
        ch1->FFAccel=0;
        ch1->FFVel=0;
        ch1->MaxI=2000;
        ch1->MaxErr=40000;
        ch1->MaxOutput=2000;
        ch1->DeadBandGain=1;
        ch1->DeadBandRange=0;
        ch1->InputChan0=1;
        ch1->InputChan1=1;
        ch1->OutputChan0=1;
        ch1->OutputChan1=1;
        ch1->MasterAxis=-1;
        ch1->LimitSwitchOptions=0x100;
        ch1->LimitSwitchNegBit=0;
        ch1->LimitSwitchPosBit=0;
        ch1->SoftLimitPos=1e+009;
        ch1->SoftLimitNeg=-1e+009;
        ch1->InputGain0=-1;
        ch1->InputGain1=-1;
        ch1->InputOffset0=0;
        ch1->InputOffset1=0;
        ch1->OutputGain=1;
        ch1->OutputOffset=0;
        ch1->SlaveGain=1;
        ch1->BacklashMode=BACKLASH_OFF;
        ch1->BacklashAmount=0;
        ch1->BacklashRate=0;
        ch1->invDistPerCycle=0.00025;
        ch1->Lead=0;
        ch1->MaxFollowingError=10000000;
        ch1->StepperAmplitude=100;
        ch1->iir[0].B0=0.002819;
        ch1->iir[0].B1=0.002819;
        ch1->iir[0].B2=0.000000;
        ch1->iir[0].A1=0.994361;
        ch1->iir[0].A2=0.000000;
        ch1->iir[1].B0=1.000000;
        ch1->iir[1].B1=0.000000;
        ch1->iir[1].B2=0.000000;
        ch1->iir[1].A1=0.000000;
        ch1->iir[1].A2=0.000000;
        ch1->iir[2].B0=1.000000;
        ch1->iir[2].B1=0.000000;
        ch1->iir[2].B2=0.000000;
        ch1->iir[2].A1=0.000000;
        ch1->iir[2].A2=0.000000;
        ch2->InputMode=ENCODER_MODE;
        ch2->OutputMode=DAC_SERVO_MODE;
        ch2->Vel=100000;
        ch2->Accel=1e+006;
        ch2->Jerk=1e+006;
        ch2->P=1;
        ch2->I=0;
        ch2->D=0;
        ch2->FFAccel=0;
        ch2->FFVel=0;
        ch2->MaxI=2000;
        ch2->MaxErr=40000;
        ch2->MaxOutput=2000;
        ch2->DeadBandGain=1;
        ch2->DeadBandRange=0;
        ch2->InputChan0=2;
        ch2->InputChan1=2;
        ch2->OutputChan0=2;
        ch2->OutputChan1=2;
        ch2->MasterAxis=-1;
        ch2->LimitSwitchOptions=0x100;
        ch2->LimitSwitchNegBit=0;
        ch2->LimitSwitchPosBit=0;
        ch2->SoftLimitPos=1e+009;
        ch2->SoftLimitNeg=-1e+009;
        ch2->InputGain0=-1;
        ch2->InputGain1=-1;
        ch2->InputOffset0=0;
        ch2->InputOffset1=0;
        ch2->OutputGain=-1;
        ch2->OutputOffset=0;
        ch2->SlaveGain=1;
        ch2->BacklashMode=BACKLASH_OFF;
        ch2->BacklashAmount=0;
        ch2->BacklashRate=0;
        ch2->invDistPerCycle=0.00025;
        ch2->Lead=0;
        ch2->MaxFollowingError=10000000;
        ch2->StepperAmplitude=100;
        ch2->iir[0].B0=0.002819;
        ch2->iir[0].B1=0.002819;
        ch2->iir[0].B2=0.000000;
        ch2->iir[0].A1=0.994361;
        ch2->iir[0].A2=0.000000;
        ch2->iir[1].B0=1.000000;
        ch2->iir[1].B1=0.000000;
        ch2->iir[1].B2=0.000000;
        ch2->iir[1].A1=0.000000;
        ch2->iir[1].A2=0.000000;
        ch2->iir[2].B0=1.000000;
        ch2->iir[2].B1=0.000000;
        ch2->iir[2].B2=0.000000;
        ch2->iir[2].A1=0.000000;
        ch2->iir[2].A2=0.000000;
        ch3->InputMode=ENCODER_MODE;
        ch3->OutputMode=NO_OUTPUT_MODE;
        ch3->Vel=100000;
        ch3->Accel=100000;
        ch3->Jerk=2e+07;
        ch3->P=0.05;
        ch3->I=0;
        ch3->D=1;
        ch3->FFAccel=0;
        ch3->FFVel=0;
        ch3->MaxI=2000;
        ch3->MaxErr=400000000000;
        ch3->MaxOutput=2000;
        ch3->DeadBandGain=1;
        ch3->DeadBandRange=0;
        ch3->InputChan0=3;
        ch3->InputChan1=0;
        ch3->OutputChan0=3;
        ch3->OutputChan1=0;
        ch3->MasterAxis=-1;
        ch3->LimitSwitchOptions=0x100;
        ch3->LimitSwitchNegBit=0;
        ch3->LimitSwitchPosBit=0;
        ch3->SoftLimitPos=1e+09;
        ch3->SoftLimitNeg=-1e+09;
        ch3->InputGain0=1;
        ch3->InputGain1=1;
        ch3->InputOffset0=0;
        ch3->InputOffset1=0;
        ch3->OutputGain=1;
        ch3->OutputOffset=0;
        ch3->SlaveGain=1;
        ch3->BacklashMode=BACKLASH_OFF;
        ch3->BacklashAmount=0;
        ch3->BacklashRate=0;
        ch3->invDistPerCycle=1;
        ch3->Lead=0;
        ch3->MaxFollowingError=10000000000;
        ch3->StepperAmplitude=100;
        ch3->iir[0].B0=0.00141172;
        ch3->iir[0].B1=0.00141172;
        ch3->iir[0].B2=0.000000;
        ch3->iir[0].A1=0.997177;
        ch3->iir[0].A2=0.000000;
        ch3->iir[1].B0=1.000000;
        ch3->iir[1].B1=0.000000;
        ch3->iir[1].B2=0.000000;
        ch3->iir[1].A1=0.000000;
        ch3->iir[1].A2=0.000000;
        ch3->iir[2].B0=1.000000;
        ch3->iir[2].B1=0.000000;
        ch3->iir[2].B2=0.000000;
        ch3->iir[2].A1=0.000000;
        ch3->iir[2].A2=0.000000;
        EnableAxis(0);
        EnableAxis(1);
        EnableAxis(2);
        EnableAxis(3);
        DefineCoordSystem(0,1,2,3);
        // If you're using fixed outputs (I.e. Kanalog output optos/FET relay drivers), you don't need to set bit direction, so the following two lines can be removed, but you will still need to modify the defines at the top of the file
        SetBitDirection(DIR_BIT0_POS,1);    // You will need to rename DIR_BIT0 to DIR_BIT0_POS at the top of the file
        SetBitDirection(DIR_BIT0_NEG,1);    // You will need to add a define for DIR_BIT0_NEG  at the top of the file
        for (;;)  //loop forever
            WaitNextTimeSlice();
            OutputSignMag(0,DIR_BIT0_POS,DIR_BIT0_NEG);              // This calls, and passes the required values to the function
    // write the servo output value to the relative DAC, and activate/deactivate direction bits depending on negative/positive output
    void OutputSignMag() //(function and args)
        if (chan[3].Enable)
            if (chan[3].Output >= 0)
                DAC(3, (int)chan[3].Output*-1);  // Set DAC output, using channel output
                ClearBit(DIR_BIT0_NEG);   // Clear negative direction bit/output
                SetBit(DIR_BIT0_POS);   // Set positive direction bit/output           //(set value '1' to 'dirbit' )
            else // else our channel output is negative
                DAC(3, (int)chan[3].Output);  // As we need an always positive DAC, we multiply by -1
                ClearBit(DIR_BIT0_POS);   // Clear positive direction bit/output
                SetBit(DIR_BIT0_NEG);    // Set negative direction bit/output
            else // else the channel is disabled so set DAC to zero, and disable both outputs
                DAC(3, 0);
     void ServiceMPG()
        static int Pos, FirstTime=TRUE;
        static int InMotion=FALSE,Axis,LastAxis=-1;
        static double LastChangeTime=0,Target,Factor=0;
        int Change1, NewPos;
        if (FirstTime)
            Pos = chan[MPG_INPUT_AXIS].Position;
            FirstTime=FALSE;
        NewPos = chan[MPG_INPUT_AXIS].Position;
        Change1 = NewPos - Pos;
        Pos = NewPos;
        if (!ReadBit(HANDWHEEL_EN) || JOB_ACTIVE) // if not button pressed or Job Active ignore the encoder.
            Change1 = 0;
        else if (ReadBit(FACTOR1))  // is X1 selected?
            Factor = 4;
        else if (ReadBit(FACTOR10))  // is X10 selected?
            Factor = 20;
        else if (ReadBit(FACTOR100))  // is X100 selected?
            Factor = 40;
        else if (ReadBit(FACTOR200))  // is X200 selected?
            Factor = 400;
        else
            Factor = 0.0;
        if (ReadBit(SELECTX))  // is x selected?
            Axis=0;
        else if (ReadBit(SELECTY))  // is y selected?
            Axis=1;
        else if (ReadBit(SELECTZ))  // is z selected?
            Axis=2;
        else if (ReadBit(SELECTA))  // is A selected?
            Axis=3;
        // check if the Axis just changed or we have been
        // converging to the target for a long time
        if (Axis != LastAxis ||
            (InMotion && Time_sec() > LastChangeTime+FINAL_TIME))
            if (InMotion)
                Move(LastAxis,Target);  //finalize any motion
            LastAxis = Axis;
            InMotion = FALSE;
        if (Change1) // did we move?
            if (!InMotion) Target = chan[Axis].Dest;
            Target += Change1 * Factor;
            MoveExp(Axis,Target,TAU);  // note: contains a WaitNextTimeSlice
            LastChangeTime = Time_sec();
            InMotion=TRUE;
        else
    Attached Thumbnails Attached Thumbnails Problem jig grinding machine.-s-l1600-jpg   Problem jig grinding machine.-jpg   Problem jig grinding machine.-jpg   Problem jig grinding machine.-jpg
  4. #40
    May 2006
    Hi vadim_cnc,
    It seems you created a function ServiceMPG() but never call it anywhere.
    Also you are passing parameters to the function OutputSignMag() that doesn't take any parameters.
    Please read this article to see if you can understand how to use Functions in C correctly
    KFLOP C Programs - Dynomotion
    You should of course remove the MPG from the DefineCoordSystem as the A axis and also in Tool Setup as the Spindle Threading Axis.
    Regards
    TK
  5. #41
    Nov 2016
    Hi, Tom!
    We are figured out with MPG and now we need to add buttons to face screen (for example radio buttons) but the version of Kmotion we use 4.34i does not have items like at Wiki PC KMotion CNC Screen Editor - Dynomotion.
    This at Wiki:
    Problem jig grinding machine.-script-option-3-png
    This is our:
    Problem jig grinding machine.-png
    Maybe need to setup something?
    Thanks and best regards!
    Attached Thumbnails Attached Thumbnails Problem jig grinding machine.-script-option-3-png   Problem jig grinding machine.-png
  6. #42
    May 2006
    Hi vadim_cnc,
    Message Actions were added in V4.34j
    See:
    Dynomotion
    Regards
    TK
  7. #43
    Nov 2016
    Thanks a lot, Tom!
    But it possible to add a radio buttons, like this?
    If it possible, how to add them?
    Best regards!
    Attached Thumbnails Attached Thumbnails Problem jig grinding machine.-jpg
  8. #44
    May 2006
    Hi vadim_cnc,
    No you can only modify the look of the existing Radio Buttons.
    The Radio buttons have special functionality, need to be associated as a group, configurable in Tool Setup and so forth.
    What exactly are you trying to do? I suppose it would be theoretically possible to implement such functionality with regular buttons and bitmap labels that interact.
    Regards
    TK
  9. #45
    Nov 2016
    Hi, Tom!
    Of course, functionality is possible to realize with regular toggle button. Radio buttons is more interesting (maybe only for me) to use with MPG, something like this:
    Problem jig grinding machine.-1-png
    Best regards!
    Attached Thumbnails Attached Thumbnails Problem jig grinding machine.-1-png
  10. #46
    Nov 2016
    One more question, can this board (KFLOP) accumulate an error while working?
    After 3 hours of the cycle in which the axis moves, the range of movement has decreased. Maybe it is associated with the old age of our equipment (such as an electric drive).
    Maybe You know something about it?
    Best regards!
  11. #47
    May 2006
    Hi vadim_cnc,
    Here is an example of how you might create that type of functionality:
    Problem jig grinding machine.-radiotypeselector-png
    This uses 3 Virtual Bits to contain the X Y Z Selection
    The X Button sets the 3 states as appropriate for X by using an Action to run a C Program like this:
    Code:
    main()
    	SetBit(1024);
    	ClearBit(1025);
    	ClearBit(1026);
    Y button runs this:
    Code:
    main()
    	ClearBit(1024);
    	SetBit(1025);
    	ClearBit(1026);
    I've attached the programs and screen script
    Z button runs this
    Code:
    main()
    	ClearBit(1024);
    	ClearBit(1025);
    	SetBit(1026);
    Does that work for you?
    Regards
    Attached Files Attached Files
    TK
  12. #48
    Nov 2016
    Hi, Tom!
    I tried this and it is works great, thanks!