    I'm totally new to modbus, so bear with me. I'm trying to start/stop and set frequency on a Yaskawa V1000 vfd over modbus rtu. Currently I'm using modpoll. I can read some stuff using modpoll so I know the communication is working. I just don't understand the addressing.

    This is from the example, red is the Start reference (1-65536, 100 is default). I'm not sure how Yaskawa address ranges work. Would I use "-r 1"? That didn't seem to work.
    modpoll -b 19200 -p none -m rtu -a 3 -r 500 -c 10 COM1

    This is the snippit from the manual.
    Yaskawa modbus rtu any working examples?-yaskawa_modbus-jpg

    Similar Threads:


  2. #2
    Member
    Join Date
    Jun 2004
    Location
    Scotland
    Posts
    355
    Downloads
    0
    Uploads
    0

    Default Re: Yaskawa modbus rtu any working examples?

    Have a read through this FAQ - Simply Modbus - About Modbus , especially the How is data stored in Standard Modbus answer.

    I'll admit Modbus addressing made my head hurt, but it's essentially to do with what address you use to access each register, as to what you actually get.



  3. #3
    Member
    Join Date
    Dec 2005
    Location
    US
    Posts
    504
    Downloads
    0
    Uploads
    0

    Default Re: Yaskawa modbus rtu any working examples?

    Quote Originally Posted by m_c View Post
    Have a read through this FAQ - Simply Modbus - About Modbus , especially the How is data stored in Standard Modbus answer.

    I'll admit Modbus addressing made my head hurt, but it's essentially to do with what address you use to access each register, as to what you actually get.
    Thanks for the Simple Modbus link. I downloaded the demo Simply Modbus Master software. It looks like I should be able to craft the messages and test the responses using that. More reading.



  4. #4
    Member
    Join Date
    Dec 2005
    Location
    US
    Posts
    504
    Downloads
    0
    Uploads
    0

    Default Re: Yaskawa modbus rtu any working examples?

    I have modpoll working. I ended up sniffing the rs-485 bus while setting the frequency with my other control and discovered I was attempting to write to the wrong register. I was attempting to write the frequency to 0002H instead of 0280H. Doh!

    Sniffed write:
    01 10 02 80 00 01 02 2E E0 86 78

    Decoded:
    01 = ID
    10 = Write command
    02 80 = d1-01 (0280) Frequency Reference 1
    00 01 = 1 Register
    02 = 2 data bytes
    2E E0 = 12000 (Set RPM)
    86 78 = CRC

    So now it's easy to use modpoll. I did also have to use PDU addressing addressing (-0).

    modpoll.exe -p none -1 -0 -r 640 -b 9600 com3 12000

    Yeah, I can now set the spindle speed.



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

Yaskawa modbus rtu any working examples?

Yaskawa modbus rtu any working examples?