I've just acquired a Tree Journeyman 310 Mill with a Dyanapath Delta 20 Controller. When I start it up I get the usual E-Stop error which I can clear. That is followed by instructions to "Reference the axes." I have been using the following procedure without success.
1) "Mode"
2) "0" (for Jog)
3) "R" (for reference)
4) "Enter" (with or without this key, no action)
5) "Start"

I get no response following these steps, which I got from a previous post. The boards inside the controller show all of the proper settings. The power is good and correct. When I loosen the cables at the servos I get limited and eratic movement. The connections are all tight and clean.

Any ideas? I'm awaiting the factory's manual arrival in the mail, but I'm not pinning all my hopes on that.
Reply With Quote

  #2   Ban this user!
Old 12-13-2009, 08:22 PM
 
Join Date: Jan 2008
Location: us
Posts: 62
donnelson is on a distinguished road

I THINIK YOU MUST FIRST MOVE THE AXES AWAY FROM THEIR STOPS THAN HIT R THAN MOVE EACH AXES BUTTON TOWARDS THE STOP IT WILL TAKE OVER AND HOME EACH AXES BY ITS SELF FOR EXAMPLE YOU MUST LOWER THE Z TOWARDS THE TABLE THAN HIT R THAN START TO MOVE IN THE POSITIVE DIRECTION AND IT WILL TAKE OVER AND HOME OUT THE Z REPEAT FOR X AND Y
Reply With Quote

  #3   Ban this user!
Old 12-14-2009, 06:41 AM
 
Join Date: Oct 2007
Location: USA
Posts: 30
kwhizz is on a distinguished road

The machine is programmed with travel limits that are preset at the factory......If you look on the Saddle and Table....you will see a round contactor that is mounted to the Table/Saddle and a electric contact switch that is solid mounted.......when you get to the reference mode.....(Move the spindle down before) .....then you hit the "X","Y' and "Z" axis travel control in the + direction......the machine should automatically move along the Axis until the Mechanical Contact hits the solid mounted switch........Make sure the feed control is not turned down............Until the Reference proceedure is performed.........The Machine doesn't know where it is or how far it can move without hurting itself.......The Home position can be changed and has nothing to do with machine reference..............Hope this helps

Ken
Reply With Quote

  #4   Ban this user!
Old 12-14-2009, 03:19 PM
 
Join Date: Sep 2008
Location: USA
Posts: 17
davidshearer is on a distinguished road

Thank you Donnelson and Kwhizz for your suggestions. But they didn't work. On closer inspection I discovered that a couple of red LEDs are lighting up inside the controller. On the "PIC" board there is a red LED on for "Run." But like the other "good" lights, I would expect it to be green. And, on the "Auxiliary" board there is a red LED for "Proc WDT Fail." Any thoughts on the matter?
Reply With Quote

  #5   Ban this user!
Old 12-14-2009, 08:25 PM
 
Join Date: Sep 2008
Location: USA
Posts: 17
davidshearer is on a distinguished road

Well, digging even deeper I have discovered that some of the output terminals on the DC voltage supply to the controller have no voltage whatsoever. This could be the problem,no? Does anyone have any idea what the output voltages should be? I read it in an earlier post, but can't seem to find it now.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 12-14-2009, 10:30 PM
 
Join Date: Jan 2008
Location: us
Posts: 62
donnelson is on a distinguished road

I THINK THEY ARE RIGHT ON THE EDGE OF THE BOARD -5 VOLTS + 5 VOLTS
THE BEST PERSON TO ASK IS PARTS AND SMARTS JULIUS IS HIS NAME I CAN GET HIS NUMBER TOMORROW VERY GOOD WITH DYNAPATH CONTROLS
Reply With Quote

  #7   Ban this user!
Old 12-17-2009, 06:40 PM
 
Join Date: Oct 2006
Location: United States
Posts: 97
jagardner4 is on a distinguished road

I regret to inform everyone that Julius Gertz passed away several months ago. He was a good friend and colleague and, yes, very knowledgeable on DynaPath controls. He will be sorely missed.

As to the voltages on a Delta 20, they are +24, +5, +15 and -15. A bad power supply could cause the WDT (watch dog timer) fault, so the power supply is a good place to start your troubleshooting.
Reply With Quote

  #8   Ban this user!
Old 12-17-2009, 07:27 PM
 
Join Date: Jan 2008
Location: us
Posts: 62
donnelson is on a distinguished road

i am sorry to hear that. now who will we look to for our support I did not even know he was ill do you know what happened to julius
don nelson
Reply With Quote

  #9   Ban this user!
Old 12-19-2009, 11:05 AM
 
Join Date: Sep 2008
Location: USA
Posts: 17
davidshearer is on a distinguished road

I count eleven terminals on the DC power supply for the controller. So which voltages go to which terminals?

And, what is the "Watch Dog Timer" (WDT) and what purpose does it serve?

Actually, I had a great phone call with Al Strelbicki of Parts and Smarts. I put the fate of my controller in his hands. I bundled the whole thing up and sent it to his shop in Wisconsin where he has agreed to troubleshoot the system for $200.00. I'm keeping my fingers crossed in hopes of a economical fix.

I too am sorry to learn of the passing of Julius Gertz.
Reply With Quote

  #10   Ban this user!
Old 12-20-2009, 07:52 AM
 
Join Date: Oct 2006
Location: United States
Posts: 97
jagardner4 is on a distinguished road

Originally Posted by davidshearer View Post
I count eleven terminals on the DC power supply for the controller. So which voltages go to which terminals?


And, what is the "Watch Dog Timer" (WDT) and what purpose does it serve?
There were a few configurations of the Delta 20 hardware, but the most common power supply wiring can be found at:

http://www.dynapath.com/page_support_powersupplies.htm

The Watch Dog Timers (WDTs) are hardware circuits, one on the PIC (programmable interface controller) and another on the main processor. If the associated processor doesn't "service" the WDT every few milliseconds, the hardware circuit trips and the CNC will go into E-Stop. In short, it's a fail-safe to make sure the processors are running and updating the servo loop. When the power supply fails, the WDTs never get reset because the processors never start up properly.
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 12-26-2009, 05:39 PM
 
Join Date: Sep 2008
Location: USA
Posts: 17
davidshearer is on a distinguished road

This just gets more interesting by the post. It just takes the right explanation, and a little while to get my mind wrapped around the ideas, for it to begin to make sense. Thanks for your input "jagardner4." I am beginning to think the root of my problem may be the DC power supply. Dynapath has an interesting idea on the why and how of power supply degradation. It boils down to aging mostly.
Reply With Quote

  #12   Ban this user!
Old 01-07-2010, 08:03 PM
 
Join Date: Sep 2008
Location: USA
Posts: 17
davidshearer is on a distinguished road
Problems Solved: For what it's worth...

Well, I sent my whole Delta 20 controller for repair to Al Strelbicki at Parts & Smarts in WI. They diagnosed a faulty DC power supply as the culprit. They also reloaded the machine parameters, which had been corrupted. It was about $1100.00 plus shipping but I have a Tree Journeyman 310 that works like a charm now. I was impressed with the level of service and knowledge at Parts & Smarts. I highly recommend them if you can't fix it yourself.

A couple of notes might be worth sharing with other novices who stumble upon this post.

1) If your machine has a feed rate override knob, don't forget to turn it on. "Off" overrides the axes feeds entirely, defeating any intended movement. (How many hours did I spend pondering this predicament; I'd hate to say)

2) If you had your parameters reset, you will most likely want to "Intilize" the machine. You don't have to do this, but it saves a heck of a lot of time by not having to reset the controller every time you accidentally travel past the machine limits. The process is described in the Dynapath manual. I know; they are expensive ($210.00), but worth every dollar if you are serious about learning what this baby can do.

I'm still pretty new to this control, but I've picked up a lot already, and I have the manual! So, if you've got a problem feel free to drop a line and I'll give you my best unqualified advice, or share a few pages from the Dynapath manual with you. But don't ask me to post the whole book. Dynapath is still in business and guards their copyright jealously.

Last edited by davidshearer; 01-07-2010 at 09:54 PM.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need Help!- dynapath delta 20 alex2008 Machine Problems, Solutions , Wireless DNC, serial port 6 11-09-2011 04:22 AM
Dynapath Delta 50 Nastyzen Dynapath 35 07-27-2011 06:46 PM
DNC w/Dynapath Delta 20 rr167 Machine Problems, Solutions , Wireless DNC, serial port 17 07-01-2011 07:46 AM
dynapath delta 20 chipman General CNC (Mill and Lathe) Control Software (NC) 5 12-15-2008 01:47 PM
dynapath delta 10 help undertowx General CNC (Mill and Lathe) Control Software (NC) 2 07-05-2006 09:49 AM




All times are GMT -5. The time now is 05:20 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361