Shop wiring

I have just moved into a new shop and I need to run wires to power some machines and welders. I have 3ph 208V at the panel. I measured the actual voltage to be 213V between phases.

Here are the machines:

Tree CNC for retrofit. 2hp 3ph spindle motor (6.2A@230V nameplate) This machine already has 30A fuses in place which I think I will keep. 5' from panel.

Bridgeport milling machine. 1.5hp 3ph spindle motor (4.4A@230V nameplate) 10' from panel.

Small shop built CNC lathe. 2hp spindle motor (6A @230V nameplate) VFD can take 1ph or 3ph. 20' from panel.

Manual lathe not yet purchased. 3hp max 3ph(10.6A@208V NEC FLA table) 25' from panel.

Miller Dynasty 350 welder 36A@208V 3ph nameplate. 30'-40' from panel.

Belt sander. 2hp 3ph (5.5A@208V nameplate). 30' from panel.

Air compressor. 7.5hp 1ph (32A@230V name plate) 65' from panel

Here are my questions:
Wires and breakers
Tree CNC - #10 THHN - 30A, 3 pole breaker.
Bridgeport - I've already wired this with #12 THHN and a 20A 3 pole breaker.
CNC Lathe - #12 THHN - 20A 2 pole or 3 pole breaker.
Manual lathe - #12 THHN - 20A 3 pole breaker.
Welder - #8 THHN - 40A breaker (Owners manual recommends 10 gauge wire with 40A time delay or 50A normal circuit breaker)
Belt sander - #12 THHN - 20A 3 pole breaker.
Air compressor - #6THHN, #6 Ground? - 50A 2pole breaker.

I would like to use two NEMA 14-50 style receptacles for the welder so I can plug it in in two places. They are rated for 50A with 3 conductors and a ground.

Should I combine any of the other circuits? For example plug the belt sander in to the welder plug or put the two lathes on one circuit. I think I need to combine at least one pair to have enough room in the panel.

What size conduit should I run? I have a hand bender for 3/4" EMT but I don't mind buying a bender for 1" or 1-1/4" EMT. Should I run everything in its own conduit, a couple bigger ones, or one big one for everything?

Should all grounds come back to panel individually or can they be daisy chained?

Wow, that is a long post. If you can contribute any help I would appreciate it.
Reply With Quote

  #2   Ban this user!
Old 01-30-2012, 11:51 AM
 
Join Date: May 2004
Location: United States
Age: 48
Posts: 2,202
txcncman is on a distinguished road

There are both national and local electrical codes that need to be met. Personally, I would always have each machine on its own circuit for safety and maintenance reasons. Yes, the more copper and disconnects and circuit breakers you buy, the more expensive it gets. But, what is expensive is liability when someone gets hurt. Also be wary of wires sizes, I have found that what is usually recommended in charts and tables is one wire size smaller than what is needed to avoid voltage drops.
__________________
http://www.kirkcon.com/
Reply With Quote

  #3   Ban this user!
Old 01-31-2012, 07:51 PM
 
Join Date: Apr 2007
Location: New York, NY
Posts: 419
will gilmore is on a distinguished road

Thanks for the reply. I've done all the reading I can and that's what I came up with. Any thoughts on conduit size?
Reply With Quote

  #4   Ban this user!
Old 01-31-2012, 08:39 PM
 
Join Date: May 2004
Location: United States
Age: 48
Posts: 2,202
txcncman is on a distinguished road

If I have to pull the wire myself, it better be huge. There are charts available that will tell how many wires of certain sizes can be run in various size conduit. The problem I have seen is that these charts do not allow "extra room" for pulling wire through 90 degree ells or 90 degree bends. A good rule of thumb might be when you put the desired wires into the conduit you can still easily get your thumb inside. This should leave enough "extra room".
__________________
http://www.kirkcon.com/
Reply With Quote

  #5   Ban this user!
Old 01-31-2012, 09:17 PM
 
Join Date: Apr 2007
Location: New York, NY
Posts: 419
will gilmore is on a distinguished road

I've come to the same conclusion about pulling. The chart says 9 #12 wires in a 1/2" EMT, yeah right. I guess I'll go 1 or 1-1/4 for the welder and air compressor and 3/4 for the other circuits.
Reply With Quote

Sponsored Links
  #6  
Old 01-31-2012, 10:21 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,536
Al_The_Man is on a distinguished road
Buy me a Beer?

Pick up a Fish Tape and Wiring Lube.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #7   Ban this user!
Old 02-01-2012, 12:09 AM
 
Join Date: Feb 2009
Location: usa
Posts: 2,913
underthetire is on a distinguished road

Look up the nfpa code. It's usually no more than a 80 percent fill on conduit, and changes for every bend in the conduit. It speced for heat dissipation in the lines.
Reply With Quote

  #8   Ban this user!
Old 02-01-2012, 08:36 AM
 
Join Date: Apr 2007
Location: New York, NY
Posts: 419
will gilmore is on a distinguished road

I've never heard anything about accounting for bends in the conduit. Do you have any more information on that?
Reply With Quote

  #9   Ban this user!
Old 02-01-2012, 10:11 AM
 
Join Date: May 2004
Location: United States
Age: 48
Posts: 2,202
txcncman is on a distinguished road

Only information I have is practical. Nothing written down. Once you get up to about #8 wire size, it does not like to bend very well. Common sense should tell you pulling 3 #8's though 1-1/2" conduit should be easier than pulling 3 #8's through 1" conduit, even though a chart (Conduit size) says you can put 9 #8's in 1" conduit.
__________________
http://www.kirkcon.com/
Reply With Quote

  #10  
Old 02-01-2012, 10:14 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,536
Al_The_Man is on a distinguished road
Buy me a Beer?

This is why you need the wiring lube,
Makes wiring a cinch, you obviously need 2 people when pulling wires.
Using the lube you don't need to cut down on wire capacity for bends, especial on wide bend EMT.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 02-01-2012, 10:27 AM
 
Join Date: Apr 2007
Location: New York, NY
Posts: 419
will gilmore is on a distinguished road

Fish tape and lube it is. Thanks everyone.
Reply With Quote

  #12   Ban this user!
Old 02-02-2012, 02:48 PM
 
Join Date: Apr 2007
Location: New York, NY
Posts: 419
will gilmore is on a distinguished road

One more question. I'm putting in two receptacles for the welder. I'm familiar with grounding boxes using a pig tail going to a screw in the box. What do I do with #6THHN wire. I don't think their are wire nuts that accept 4 #6 wires.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Shop Wiring Question BanduraMaker DIY-CNC Router Table Machines 8 03-13-2011 02:27 PM
Problem- job shop jeanro49 GibbsCAM 0 10-30-2010 11:03 AM
Need Help!- OLD SHOP BOT PR shovelhead3d General Electronics Discussion 1 11-21-2008 03:20 PM
Shop wiring advice 91bird General Electronics Discussion 11 10-16-2008 11:47 AM
Best cad cam for our shop??? mt92 General CAM Discussion 3 10-16-2005 02:02 AM




All times are GMT -5. The time now is 04:10 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361