    estop diagram

    anyone know of e stop diagram, that use a contactor to remove main feeds
    but keeps pc power


  2. #2
    Registered Karl_T's Avatar
    Join Date
    Mar 2004
    Location
    Dassel,MN,USA
    Posts
    1,361
    Downloads
    0
    Uploads
    0
    I don't have anything to sketch into a PC handy.
    The circuit is easy to describe. You need a NO pushbutton, labled reset. Attach it to power and then to the coil on a double pole relay,labled MCR for master control relay. Now put Estop circuit power to one of the poles on MCR. From the NO side of this pole, wire all your Estop buttons in series and then terminate at the MCR coil.

    How it works: push reset button and MCR coil closes. When button is released, the coil is latched in because power is now going through the NO contact and through all the Estop buttons back to the coil. Push an Estop button and the circuit is broken, openning the MCR coil.

    Now, take the other pole on MCR and put it in front of any coils or relays you want to break when the Estop is pressed.

    Karl


  3. #3
    Registered solodex2151's Avatar
    Join Date
    Nov 2006
    Location
    USA
    Posts
    226
    Downloads
    0
    Uploads
    0
    The circuit in the Picture is what is used in industry. I was really lazy and did not draw it in Ladder Logic form, but you get the idea. Your start pushbutton is momentary. Your emergency stop should be a NC swtich that is closed when the button is pulled out (very important because you can bump it with a body part to shut off the machine versus having to pull it out.

    When the emergency stop is closed and you press the start push button, the K1 coil is activated and its contacts close. When you release the start pushbutton, the coil is still actuated by itself through one of its contact pairs. The second contact pair is used to supply mains power to your equipment. If you press the emergency stop, the switch stops actuating the coil the mains power is cut off to the equipment. In order to start the machine again, you must first pull the emergency stop out so it closes and then push the start button again.
    Attached Thumbnails Attached Thumbnails estop diagram-emergency_power_circuit.png  


  4. #4
    Registered
    Join Date
    Mar 2008
    Location
    out here
    Posts
    36
    Downloads
    0
    Uploads
    0
    what controls yours s2, im also assuming your using twist locking e-stop switches? not sure if the start button would be need in that case? but
    depressing and (twist) releasing the locked estop state?


  • #5
    Registered solodex2151's Avatar
    Join Date
    Nov 2006
    Location
    USA
    Posts
    226
    Downloads
    0
    Uploads
    0
    It is a standard estop button that pulls out and pushes in. The closed state should be when the button is pulled out. Then, all you have to do is push it in to stop the machine. This is real handy especially if a body part like your hand gets stuck in the machine. Then all you really have to do it whack the estop with whatever you can (knee, foot, torso, etc) to shut it off. It will then stay depressed until the operator physical pulls it out again.

    This button is what I am talking about.

    You do need the start button. The E-Stop should NEVER be the button that applies power to the system. It's sole function in life is to disconnect power to the system as quickly as possible. This combination is what is known as a manual reset.

    I would also be tempted to kill computer power with this. The E-Stop should only be pressed in an emergency. An emergency would be when a body part is caught in the machine, the material breaks free of its hold downs and is spinning wildly threatening to hurt someone, etc. I also realized that it should really just kill power and if the relay contacts fuse closed, we're in trouble. So, take a look at the circuit below. The E-Stop breaks mains power completely. You have you start circuit for the manual reset, along with a stop button. The stop button will kill power to the motors and the router so you can do things like bit changes, adding parts, etc. in a safer manner. However, it doesn't kill the computer power, just power to anything with potential energy.

    Does this help to answer you questions?
    Attached Thumbnails Attached Thumbnails estop diagram-emergency_power_circuit.png  


  • #6
    Registered solodex2151's Avatar
    Join Date
    Nov 2006
    Location
    USA
    Posts
    226
    Downloads
    0
    Uploads
    0

    NEMA specifications on E-Stops

    Markus,

    I thought I would included the industry code for E-Stops. This is NFPA 79, and if you read 9.5 thru 9.63 it will explain the 3 kinds of stops.

    Category 0: immediate removal of power to all machine actuators...ie unctrolled stop.
    Category 1: a controlled stop with power to the machine actuators available to achieve the stop then power is removed.
    Category 2: a controlled stop with power left available to machine actuators.
    Each machine shall be equipped with a Category 0 stop.

    9.6.3 Emergency Stop
    --It shall override all other functions and operations in all modes

    --Power to the machine actuators that can cause a hazardous condition(s) shall be removed as quickly as possible without creating other hazards (e.g. by the provision of mechanical means requiring no external power.

    --Reset shall not initiate a restart

    The estop shall function as either Category 0 or Category 1. The choice of category of estop shall be determined in accordance with the requirements of the application.

    Where a Category 0 stop is used it shall have only hardwired electromechanical components. Its operation shall not depend on electronic logic or the transmission of commands over a network.

    Where a Category 1 stop is used for the estop final removal of power to the machine actuators shall be ensured and shall be by means of electromechanical components.


  • #7
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,951
    Downloads
    0
    Uploads
    0
    Quote Originally Posted by solodex2151 View Post
    Markus,

    I thought I would included the industry code for E-Stops. This is NFPA 79, and if you read 9.5 thru 9.63 it will explain the 3 kinds of stops.
    Most of these E-stop conditions are now done with a special relay called a Safety Relay for controlled power-down/up, almost all European equipment has them and N.Am. is now coming on board.
    In the systems I install, I prefer to leave the PC or controller powered, I E-stop all output functions = power to any solenoids,spindle contactors etc
    I also use auxiliary contacts on a the main E-stop relay to all the drive enable inputs. If you switch off the drive power, the DC takes a while to decay, so this method stops the drives immediately, also a contact can be used to indicate to the controller that an E-stop has occurred.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • Similar Threads

    1. Estop and limits
      By krymis in forum General Electronics Discussion
      Replies: 1
      Last Post: 02-18-2008, 06:39 PM
    2. need estop wiring diagram and how to for limit switches
      By eloid in forum CNC Wood Router Project Log
      Replies: 2
      Last Post: 11-05-2007, 09:55 PM
    3. random estop
      By erase42 in forum DeskCNC Controller Board
      Replies: 21
      Last Post: 02-02-2007, 06:28 PM
    4. ESTOP keeps happening
      By klick0 in forum LinuxCNC (formerly EMC2)
      Replies: 2
      Last Post: 12-17-2005, 12:06 PM
    5. Estop
      By HuFlungDung in forum CamSoft Products
      Replies: 5
      Last Post: 03-06-2004, 02:24 PM

    Posting Permissions


     


    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.