Hi Guys just a quick newbie question about how to use shielded cable and limit switches. When wiring limit and home switches up what do I do with the shield part of the cable, Do I solder the inner part to the contacts & bob. do I just leave the shield at the switch & bob end or does one end or both need to be grounded some how. Had a search but got even more confused as to what is needed. cheers for any pointers KAT |
|
#2
| ||||
| ||||
| dont quote me on this (im just in the process of doing the same thing myself). but i think what you have to do is leave the switch side of the shield as it is (do not connect it to anything), and then connect the shield on the other end (driver side) to your main ground earth point. earthing both ends of the shielded braid can cause feedback loops and undesired problems with your motor operation. though theres different kinds of cable |
|
#3
| |||
| |||
|
|
#4
| ||||
| ||||
| There has been a recent reversal in the old method of grounding one end only. See section 6 of the pdf. http://www.automation.siemens.com/do.../emv_r.pdf?p=1 concerning grounding shielding both ends. Al.
__________________ CNC, Mechatronics Integration and Machine Design. “Logic will get you from A to B. Imagination will take you everywhere.” Albert E. |
|
#6
| ||||
| ||||
| What about automotive dielectric silicone grease? Al.
__________________ CNC, Mechatronics Integration and Machine Design. “Logic will get you from A to B. Imagination will take you everywhere.” Albert E. |
|
#7
| ||||
| ||||
| sorry action-kat, dont mean to hijack this thread, but i think its along the same lines.. going by the seimens guidelines you posted al.. they suggest putting a shield up bewteen the transformer and data carrying lines of the stepper motor drivers in the control box.. would an earthed metal plate in the attached photo act as a emi shield when placed between the 'victim' and the emmiter..?(the driver cables and the transformer toroid) |
|
#8
| ||||
| ||||
| Historically the metal shield to prevent E.M. radiation has been mµ metal. Mu-metal - Wikipedia, the free encyclopedia But this is usually reserved for very sensitive applications such as medical equipment etc. In the case you have shown, any metal that is electrically permeable should help. One advantage of a Toroidal transformer is it does not radiate EMI to the extent a EI core type does. The magnetic field tends to stay contained within the transformer itself. Al.
__________________ CNC, Mechatronics Integration and Machine Design. “Logic will get you from A to B. Imagination will take you everywhere.” Albert E. |
|
#9
| |||
| |||
What Siemens are describing is a rather sophisticated grounding SYSTEM that still relies on a central single point ground. You can do it their way, but you will need to know exactly what you are doing or it can go horribly wrong. If you building or modifying your own system and do not have 10 - 20 years experience in this area, the standard ground-at-one-end rules are much easier and safer to follow. Cheers |
|
#10
| ||||
| ||||
| you're right ground at one end is simpler, but the siemens guidelines arent that complicated they just go in for page after page.. they dont need 10-20 years experience to understand and implement them, dont be phazed.. keep youre cables as short as possible, seperate your power and signal cabling, be aware of the different electromagnetic fields that your components emmit and,, the componenets that they will effect the most, and you should be ok. Last edited by neurofen; 01-14-2011 at 07:44 PM. |
| Sponsored Links |
|
#11
| ||||
| ||||
| Also what they are espousing is uni-potential bonding. I don't think there is anything especially sophisticated about it. It helps to be aware of the concept involved as to using Earth as a ground conductor. The original concept was Early developers of electrical systems theorized that the earth was an electrically neutral body, i.e. an equal number of negative and positive charges are distributed throughout the earth at any given time. Being electrically neutral, earth is considered to be at zero potential and establishes a convenient reference frame for voltage measurements. So simply put, the effort is, is to make all Earthed grounded parts of the system common to each other. Al.
__________________ CNC, Mechatronics Integration and Machine Design. “Logic will get you from A to B. Imagination will take you everywhere.” Albert E. |
![]() |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | Search this Thread |
| Display Modes | |
| |
Similar Threads | ||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| limit switches fitting and wiring | deannos | DIY-CNC Router Table Machines | 17 | 02-13-2010 05:26 PM |
| Wiring home and limit switches | Hack | General Electronics Discussion | 7 | 01-24-2009 03:47 PM |
| limit switch wiring with shielded cable | endgrainguy | General Electronics Discussion | 17 | 05-05-2008 12:22 AM |
| need estop wiring diagram and how to for limit switches | eloid | CNC Wood Router Project Log | 2 | 11-05-2007 08:55 PM |
| Wiring IH limit switches | Shepard | Industrial Hobbies (Support forum) | 10 | 03-20-2007 08:28 PM |