puma 10s not ready status

Results 1 to 5 of 5

Thread: puma 10s not ready status

  1. #1
    Member
    Join Date
    Mar 2016
    Location
    Palestinian Territory, Occupied
    Posts
    36
    Downloads
    0
    Uploads
    0

    Default puma 10s not ready status

    hi,
    i have entered parameters for puma 10s machine, and have this status "not ready". the manufacturer doesn't have a complete list. may be i still need more parameters, who can help me? who is familiar with fanuc otc controller .
    best regards

    Similar Threads:
    Attached Thumbnails Attached Thumbnails puma 10s not ready status-20160618_171722-jpg  


  2. #2
    Member dhardt's Avatar
    Join Date
    Feb 2013
    Location
    United States
    Posts
    788
    Downloads
    0
    Uploads
    0

    Default Re: puma 10s not ready status

    When you press the button requesting Machine Ready, what happens?
    1. If nothing, press and hold the ALARM RESET button and also press the Machine Ready button.
    a. If still "nothing happens" check all E-Stop and its wiring.
    b. Possible issue with the <Machine Ready> or <ALARM RESET> buttons.
    2. If <Machine Ready> flashes and turns solid, but turns off when <ALARM RESET> is released, then you are in OVERTRAVEL
    3. IF <Machine Ready> flashes for 5 seconds and then turns off, the phase is backwards.

    No longer with Doosan Machine Tools America
    darrylhardt@gmail.com


  3. #3
    Member
    Join Date
    Mar 2016
    Location
    Palestinian Territory, Occupied
    Posts
    36
    Downloads
    0
    Uploads
    0

    Default Re: puma 10s not ready status

    thanks my friend,
    have you got the files i have attached in the previous thread?. but i didn't try to press ready button, is it clear button to catch ?
    i will try these procedures and inform you what will happen
    do you think that the entered parameters are sufficient and their values are true?
    by the way, the spindle drive status is ready as it shows 000000, and the pump work after seconds from the power on.
    thanks again for your collaboration
    best regards



  4. #4
    Member
    Join Date
    Mar 2016
    Location
    Palestinian Territory, Occupied
    Posts
    36
    Downloads
    0
    Uploads
    0

    Default Re: puma 10s not ready status

    hi, i have conducted the procedure you have sent, at the beginning, no lights appear on the ready button, there is a 2 7-seg digits, it shows 01 , i checked the emergency switch, there was no 24vdc at normally open state and no changes at the diagnostic or ladder pages , i tried to catch the second sensors that i think are connected serially, i didn't find them. finally i made a short circuit between the 24n and EMT wire inside the cabinet , which i think it is the equivalent for the emergency switches. then i tried to push the ready button, it lights all the time as flasher , even if i press alarm reset, the not ready state still flashes,
    the 7-seg digits, shows 12, when i press ready it gives 7.
    best regards
    so, what do you think the problem,
    btw, when i tried to change phases, the pump didn't work.
    best regards



  5. #5
    Member
    Join Date
    Mar 2016
    Location
    Palestinian Territory, Occupied
    Posts
    36
    Downloads
    0
    Uploads
    0

    Default Re: puma 10s not ready status

    sir,
    please do you have any answers?



Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  