    CNC - PC hardware location

    Getting ready to build a stand for my CNC lathe.

    Is it best to keep PC and CNC components in separate cabinets to minimize cross component noise or can they both reside in same cabinet?

    Thanks
    FannBlade


  2. #2
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,943
    Downloads
    0
    Uploads
    0
    I have used both methods with no problems, although of late I have tended to use Panel PC's, these are panel mount monitors and PC's in one compact package at the operator station.
    The majority of commercial systems use one enclosure with no problems and they all start out with 5v logic module controller.
    As long as the proper earth grounding and bonding is observed, you should have no problems.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  3. #3
    Registered FannBlade's Avatar
    Join Date
    Jun 2011
    Location
    USA
    Posts
    521
    Downloads
    0
    Uploads
    0
    Thanks Al that help alot it's amazing how much planning is needed on just the stand.

    Also I will be using 2 VFD's and 2-3 phase motors. Would shielded wire be enough to eliminate problem there?

    Speaking of grounding I ran a 100 AMP service to my shop from the house, it's around a 150' run, would it be advantageous to install another ground rod where it enter the shop?


  4. #4
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,943
    Downloads
    0
    Uploads
    0
    I have always made sure the VFD motor conductors are tightly wound if individual conductors, the earth ground should run alongside from VFD to motor frame.
    I have one installation with 3 VFD's running in the panel, I generally exit the panel the shortest way and use liquid seal metallic conduit to run the motor conductors in, this acts as shielding.
    You should not need a ground rod as long as your earth conductor is the right size.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


Similar Threads

  1. your location & need help :) ????
    By mcx101 in forum DIY CNC Router Table Machines
    Replies: 2
    Last Post: 03-11-2011, 03:59 PM
  2. Getting the X and Y of my First CAM location
    By vpcnc in forum BobCad-Cam
    Replies: 4
    Last Post: 06-22-2007, 10:34 AM
  3. Map your location
    By Rekd in forum CNCzone Club House
    Replies: 20
    Last Post: 10-20-2005, 10:49 PM
  4. location
    By mocnc in forum DIY CNC Router Table Machines
    Replies: 15
    Last Post: 04-08-2005, 05:12 PM
  5. location?
    By fastolds in forum Surfcam
    Replies: 11
    Last Post: 12-02-2004, 02:58 AM

Posting Permissions


 


About CNCzone.com

    We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

Follow us on

Facebook Dribbble RSS Feed


Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.