    Haunted monitor ?

    At first I thought the house was haunted, but I'd be very grateful for help analysing the following problem.

    First, about 6 weeks ago, we went on an economy drive after the last electricity bill. Using a plug in metered socket, I discovered the workshop monitor/pc which I thought switched off when I hit the off button, was still drawing about 0.3 amps, 24/7. So I switched it off at the mains as well.
    Then we noticed the electric blanket(the bedroom sockets are through the wall to the workroom sockets) didn't work properly, after 8 months with no problems. Most of the time the neon(?) dial illuminator was flickering, and the blanket might or might not get warm. Appeared to be random.
    So that went back to the supplier and exchanged for a new one.
    That seemed OK for about 4 days, then stopped working. The power neon was on, but no heat developed.
    (It has an electronic timer/controller.)

    Then we noticed the clock/radio in the bedroom was playing up, with either the dro flickering or the clock minute indicator cycling every 5 seconds.

    Haunted house?

    I've tracked it down so far to the fact that if the monitor is switched on at the socket and on standby, the clock/radio and the electric blanket work normally.
    The same is true wherever the clock is taken to in the house.
    Nothing else plugged into the socket has the same effect as the monitor.
    I've tried surge protected strip sockets as well, but nothing alters the effect of the monitor.

    When it's on standby, the clock and blanket work. When it's switched off, they don't.

    Haunted monitor ? In use with the PC it appears to work completely normally.

    Any ideas ?

    It would be some help if I new what type of load the monitor is presenting when on standby, so that I might emulate the load to see if that's the root of the problem.

    Thanks
    John
    It's like doing jigsaw puzzles in the dark.
    Enjoy today's problems, for tomorrow's may be worse.


  2. #2
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,940
    Downloads
    0
    Uploads
    0
    I see you are in the UK so probably have a 13A Ring Main system for sockets?
    I would suspect a defective connection or wiring of the PC socket, How do you turn the monitor off at the mains?
    Does the socket have switched type outlet?
    Reconnect or replace the PC socket for starters.
    If this does not cure it, I suggest moving as you may well have a haunting.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  3. #3
    Registered greybeard's Avatar
    Join Date
    Jun 2005
    Location
    UK
    Posts
    1,386
    Downloads
    0
    Uploads
    0
    Hi Al, thanks a bunch re moving

    What I have been doing today is 1. I took the clock to the furthest socket, 50 yds to the bottom of the garden - no change.
    2. All the wall sockets(switched) are on the same ring, but not the cooker, and that has a separate socket, so I plugged in there - still no change.

    3. I ran a cable from the monitor power plug to another socket on the lower floor, but again, no change, nor than taking the clock to an outhouse socket.

    It seems that wherever the clock is plugged in, it can detect the fact that the monitor is also plugged in !
    Action at a distance ??

    I do have a 'scope, and yesterday fired it up and got the usual mains pick-up on the probe lead.
    However, if I got hold of the end of the probe wire, I could see a lot of RF on top.
    Now this may be normal, with me acting as an ariel for the nearest transmitter.
    I'm a bit out of my depth here, not being a radio man, but I did wonder if a fault in the clock/radio is producing some RF which is upsetting the clock electronics, as well as the electric blanket controller incidentally, but by plugging in the monitor I'm adding a sink for the RF.
    This is getting close to mumbo jumbo, but it may spark an idea in someone.
    Regards
    John
    It's like doing jigsaw puzzles in the dark.
    Enjoy today's problems, for tomorrow's may be worse.


  4. #4
    Registered
    Join Date
    Jul 2005
    Location
    Canada
    Posts
    11,960
    Downloads
    0
    Uploads
    0
    Do you have a dimmer control or anything with an electronic thermostat anywhere in the system? I came across a funny situation once where a heater was injecting a signal into the wiring and this was affecting a numerical counter display in another location.

    For a while the situation was not funny; the counter was on a Gieger Counter and you can imagine the reaction when that suddenly started accumulating counts.
    An open mind is a virtue...so long as all the common sense has not leaked out.


  • #5
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,940
    Downloads
    0
    Uploads
    0
    Quote Originally Posted by greybeard View Post
    It seems that wherever the clock is plugged in, it can detect the fact that the monitor is also plugged in !
    Action at a distance ??
    Obviously the radio & blanket should not depend on the monitor to work.?
    Both should work in a stand alone condition, try plugging into a neighbors outlet just for the heck of it.
    It is beginning to sound like VooDoo rather than Mumbo Jumbo.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #6
    Registered greybeard's Avatar
    Join Date
    Jun 2005
    Location
    UK
    Posts
    1,386
    Downloads
    0
    Uploads
    0
    Yes, I'd thought that that might be my next trial.
    I've just been talking to the blanket service people who think that RF on the mains shouldn't affect the controller, but that just may be that they've never come across it before, so open mind still on that one.
    we'll also see if we can borrow a simillar clock/radio, to see if it's only ours that does it.
    I think that if it is, then it's bin time for the clock. If not, then.........?
    John
    It's like doing jigsaw puzzles in the dark.
    Enjoy today's problems, for tomorrow's may be worse.


  • #7
    Registered greybeard's Avatar
    Join Date
    Jun 2005
    Location
    UK
    Posts
    1,386
    Downloads
    0
    Uploads
    0
    OK, I suppose it has now got worse.
    If I take my clock/radio next door and plug it in, it can detect if my crt monitor is plugged in as well !!!!!!!!!!!!!!!!!!!!!!

    We're probably on the same phase, but that does knock on the head my idea of a monitor acting as an RF sink.

    Another appalling thought. I've just bought a new breadmaker as mine has gone berserk after seven years faithful service. That works on timing circuits too. At least I haven't thrown it away nor converted it into something else.

    Update.
    As of ten minutes ago, it now works perfectly, and I've no idea why.
    Left baffled and drained. Will now make large G&T and sit in the summerhouse wondering why life is so difficult.
    Last edited by greybeard; 06-25-2008 at 12:49 PM. Reason: update
    It's like doing jigsaw puzzles in the dark.
    Enjoy today's problems, for tomorrow's may be worse.


  • #8
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,940
    Downloads
    0
    Uploads
    0
    The puzzling thing to me is that you say they only work when the Monitor is ON or standby??
    I can see the reverse being a problem.
    Your tests seem to indicate it is mains-borne rather than RF-borne.
    Many modern monitors & TV.s have switching supplies and often this is on all the time to enable the electronic start circuit.

    One of the most bizarre problems I had many years ago in the UK was a customer that complained her TV soap opera was 1 week behind her neighbor.
    And she was right!
    But that is another story.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #9
    Registered greybeard's Avatar
    Join Date
    Jun 2005
    Location
    UK
    Posts
    1,386
    Downloads
    0
    Uploads
    0
    OK. About 30 mins ago, even though the monitor was off(see update on #7), with the clock working, the bed remade and the blanket on and warming up, everything seemed to have reverted to normal.
    I then went into the work room and reconnected everything in my workstation(desktop/printer/monitor/scanner), and turned the power switch on.
    15 mins ago, I noticed the clock, down here with me keeping an eye on it, has now started playing silly bu##ers again. The blanket is cooling down.
    Turned the blanket controllers off, and the switch on the wall socket.
    Came downstairs and 10 mins later the clock is now OK.
    It's like doing jigsaw puzzles in the dark.
    Enjoy today's problems, for tomorrow's may be worse.


  • #10
    Registered
    Join Date
    Apr 2007
    Location
    USA
    Posts
    766
    Downloads
    0
    Uploads
    0
    Has the house been checked for faulty grounds? Is that earth grounds (or maybe earths) for you brits? That seems like one of the most likely reasons for something this crazy of the top of my head. I'm thinking that something that has a bad ground connection is getting a weak but usable ground through the monitor.


  • #11
    Registered greybeard's Avatar
    Join Date
    Jun 2005
    Location
    UK
    Posts
    1,386
    Downloads
    0
    Uploads
    0
    Hi Cameron, and welcome to the seriously crazy house.
    Like most clock/radios here, it's double insulated with only twin connection and no earth.
    Likewise the electric blankets - no earth leads.
    John
    It's like doing jigsaw puzzles in the dark.
    Enjoy today's problems, for tomorrow's may be worse.


  • #12
    Registered
    Join Date
    Jul 2005
    Location
    UK
    Posts
    447
    Downloads
    0
    Uploads
    0
    assuming its noise the monitor clearly isnt the root cause of the problem, so have you tried disconnecting everything else plugged in apart from the clock(like heating, appliances etc) to see if one of them is responsible?


  • Page 1 of 5 1234 ... LastLast

    Similar Threads

    1. mazak monitor
      By rhurt in forum General Electronics Discussion
      Replies: 11
      Last Post: 03-29-2010, 11:20 PM
    2. monitor
      By rusticr6 in forum Haas Lathes
      Replies: 7
      Last Post: 10-24-2007, 08:06 PM
    3. monitor
      By CASTLEVILLE in forum Bridgeport and Hardinge Mills
      Replies: 8
      Last Post: 10-10-2007, 07:37 PM
    4. haunted by Z.1
      By kesparate in forum Esprit
      Replies: 1
      Last Post: 07-09-2007, 12:55 PM
    5. BP Series 1 with LCD monitor
      By ahmedrehan in forum Bridgeport and Hardinge Mills
      Replies: 16
      Last Post: 02-25-2007, 03:41 PM

    Posting Permissions


     


    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.