Earth grounding question

I am electrically challenged folks. Now with that said I would like some info on earth grounding. I am building a new 5 x 10 plasma table and will use a Hypertherm plasma. I know everything (plasma, table, computer and anything else that is going to be worked w/ the system) needs to be individually earth grounded to eliminate noise. The plasma will run off 240V single phase - that is 2 hots and a ground back to power panel. How do I hook up an earth ground??? Do I unhook the ground to power cabinet? Do I run another ground wire to the ground lug in the plasma and run it to ground and leave the ground to power cabinet or what????
I run an air hammer in my shop that has a 10 HP single phase motor on the monster. I will also earth ground this equipment the same way I will the plasma. Thanks for any help folks.
Reply With Quote

  #2  
Old 08-19-2008, 04:34 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,533
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by plain ol Bill View Post
I know everything (plasma, table, computer and anything else that is going to be worked w/ the system) needs to be individually earth grounded to eliminate noise. The plasma will run off 240V single phase - that is 2 hots and a ground back to power panel. How do I hook up an earth ground??? Do I unhook the ground to power cabinet? Do I run another ground wire to the ground lug in the plasma and run it to ground and leave the ground to power cabinet or what????
I am not sure what you mean by individual grounded, the general rule is to try to make everything a common ground, i.e. no difference, potential wise between ground points.
Manuf. like Messer MG systems that have used PC control systems and Hypertherm Plasma units with High frequency ignition successfully, and have used the same procedure that I use with my PC based systems.
First, the service ground and the plasma common (table) is usually taken to a ground stake at the table location, using a sufficiently large gauge cable.
The plasma power supply has to be isolated via a transformer in the hypertherm Plasma unit in order to ground the plasma positive electrode and allow it to be common to earth ground and the table, otherwise it would blow the power supply.
In the electrical enclosure, the PC ground and other auxiliary power supply commons,servo supply commons, are connected to a copper ground plate, together with all encoder shields etc.
This is also bonded to the ground stake.
Often the problem comes when an attempt is made to keep everything totally isolated and separate, instead of common bond.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 08-19-2008, 08:01 PM
Karl_T's Avatar  
Join Date: Mar 2004
Location: Dassel,MN,USA
Posts: 1,318
Karl_T is on a distinguished road

Al, That plasma is going to have both AC nuetral and a ground.

I treat AC nuetral as its own hot wire. They are connected only to the nuetral that goes back to the breaker panel.

AC nuetral carries current. Connecting it to common ground within the machine can cause trouble from my understanding. correct?

Karl
Reply With Quote

  #4  
Old 08-19-2008, 08:42 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,533
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by Karl_T View Post
I treat AC nuetral as its own hot wire. They are connected only to the nuetral that goes back to the breaker panel.

AC nuetral carries current. Connecting it to common ground within the machine can cause trouble from my understanding. correct?
I am not sure what you mean by the 'AC neutral as its own hot wire'
The plasma unit is being fed from 240v which is referenced to ground at the grounded neutral point at the panel, whether the neutral is being used or not. In this case it is probably not.
I am not advocating connecting the service ground and neutral at any place other than the panel. So the neutral does not really come into play here as a conductor.
If the table, (Plasma common) is connected to ground then it will be, or should be at the same potential as the service ground.
By bonding all grounds at one point ensures that the ground potential between any ground point is zero.
It is imperative that any ground conductor does not intentionally carry current, the general idea behind grounding is that it creates a stable reference point.
Because a conductor is grounded does not necessarily mean it is carrying ground current.
I found that grounding is one of the least understood aspects of a machine installation.
The Siemens PDF I attached to a recent posting on grounding explains Uni-potential grounding in detail.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 08-20-2008, 10:16 AM
Karl_T's Avatar  
Join Date: Mar 2004
Location: Dassel,MN,USA
Posts: 1,318
Karl_T is on a distinguished road

Originally Posted by Al_The_Man View Post
I found that grounding is one of the least understood aspects of a machine installation.
The Siemens PDF I attached to a recent posting on grounding explains Uni-potential grounding in detail.
Al.
Al I did a google search and didn't find this post. Could you give me a link to this seimens .pdf?

Karl
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 08-20-2008, 11:59 AM
 
Join Date: Nov 2007
Location: USA
Posts: 279
plain ol Bill is on a distinguished road

Yes please put a link up to that post for us Al. The more I read the more confuseder I gets. Me thinks I just may have to call a friend that was an electrician in an earlier life.
Reply With Quote

  #7  
Old 08-20-2008, 02:41 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,533
Al_The_Man is on a distinguished road
Buy me a Beer?

I forgot, I put it on a download site because of the size: http://www.divshare.com/download/5002681-38f
Here is the posting http://www.cnczone.com/forums/showthread.php?t=61657
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
grounding question, PC case ground Fiero Addiction CNC Plasma and Waterjet Machines 2 08-16-2008 07:40 AM
Grounding question! GibbonsRock Automation Technology Products 3 07-21-2008 07:39 AM
Grounding question dmparrott General Electronics Discussion 2 08-23-2007 08:50 AM
Earth Ground LYN BYRD Milltronics 5 06-20-2007 11:39 AM
How on earth do I make this!!! disinformation G-Code Programing 14 10-11-2006 07:53 AM




All times are GMT -5. The time now is 02:49 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361