Exclamation NEED HELP Arrow 750 2100 Controls Air Pressure Switch Problems

Hello to all. I am trying to figure out what is happening with my Arrow 750. When I power up, the display shows the NCA Air Pressure Alarm for switch PS_AIR_SYS(I00:00/01). I have temporarialy jumped the 4 air pressure switches on the back off with no luck. Also, this machine has the DropsA oil lube unit installed. The LED lights that show pump healthy etc. do not light up. Any ideas on what could be causing these problems?? Any advice will be greatly appreciated.
Reply With Quote

  #2   Ban this user!
Old 03-22-2011, 11:40 PM
 
Join Date: Mar 2011
Location: USA
Posts: 88
maver1ck is on a distinguished road
Buy me a Beer?

That alarm sounds like the primary air pressure switch (see pic), not one of the switches that is part of the Dropsa unit.

Just follow your main air line into the machine, and there will be a pressure swtich as part of the regulator assembly.
Attached Thumbnails
Click image for larger version

Name:	pressure switch.jpg‎
Views:	32
Size:	150.4 KB
ID:	129656  
Reply With Quote

  #3   Ban this user!
Old 03-23-2011, 09:58 AM
 
Join Date: Mar 2011
Location: USA
Posts: 7
Industrial Tool is on a distinguished road

The main air supply pressure switch was the first to get jumped. Even with it, and the others jumped, the NCA Air Pressure alarm still pops up.
Reply With Quote

  #4   Ban this user!
Old 03-23-2011, 10:16 PM
 
Join Date: Mar 2011
Location: USA
Posts: 88
maver1ck is on a distinguished road
Buy me a Beer?

Sorry, I misread your post to say you only did the switches on the Dropsa unit.

The alarm means the control is not seeing the 24V signal from the pressure switch, so I'd start with figuring out where in this chain you are losing the voltage.

There's not much in this circuit, start by checking to make sure you have +24VDC at the switch. If not, check for voltage on 424A. If this is +24, then check wire 1002-1 (pin 1 on the R1/P1 plug if your prints are the same as mine).

If you don't have +24 on 424A, you probably have a short somewhere bringing your whole 24V circuit to 0. If this is the case, start going through your prints and determining what else is drawing power on 424A. Disconnect these items individually to determine where the short is.

If you have voltage at the switch, check if it is being lost on 1002-2 (pin 2 of the R1/P1), etc, until you find where it is dropping out.
Attached Thumbnails
Click image for larger version

Name:	I0_0.jpg‎
Views:	28
Size:	23.6 KB
ID:	129729  
Reply With Quote

  #5   Ban this user!
Old 03-23-2011, 11:42 PM
 
Join Date: Mar 2011
Location: USA
Posts: 88
maver1ck is on a distinguished road
Buy me a Beer?

Originally Posted by maver1ck View Post
If you don't have +24 on 424A, you probably have a short somewhere bringing your whole 24V circuit to 0. If this is the case, start going through your prints and determining what else is drawing power on 424A. Disconnect these items individually to determine where the short is.
I jumped to this a little to quickly because I've seen 24V shorted in these machines a few times. If you don't have voltage on 424A, check the obvious things first, fuse, power supply, etc....before you start chasing down non-existent shorts.

And, once I thought about it I was getting a different alarm in those previous cases. If you have a short on the 24V, you shouldn't be able to power-up control up since the machine uses +24 to pull in TR1 for control power.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 03-24-2011, 11:40 AM
 
Join Date: Mar 2011
Location: USA
Posts: 7
Industrial Tool is on a distinguished road

I replaced the 24V Power Supply within the last month. I checked the +24V on 1002 at the pressure switch, nothing. I ohmed out the 1002 wiring and showed continuity. Went to the Input Board, nothing at the board on 1002. Checked the new PS, it has 23.8V. Went to 424A at F9, 23.8V. Went to CB1, 23.7V. Followed 424A to the Input Board, 23.7V at TB3-1. I looked at the circut on the board and didnt see any breaks in this feed.
Reply With Quote

  #7   Ban this user!
Old 03-24-2011, 02:50 PM
 
Join Date: Mar 2011
Location: USA
Posts: 88
maver1ck is on a distinguished road
Buy me a Beer?

Assuming your machine uses the same prints as mine, if you have power on 424A at TB3_1, but don't have it on P1/R1, my next guess would be something on the input board.

It looks like you should should be able to remove 424A from TB3_1 and remove plug 1. If you check TB3_1 to pin 1 on R1 what do you see. If there's nothing there, either a bad connection to pin 1, or internal break on the circuit board.

Start by thoroughly checking the wires/connectors on P1/R1 to ensure you have good contact. I have seen some of these boards burn out the circuit path on the backside (although I think that was always on the 110V), so if you haven't pulled the board and checked the back side, it wouldn't hurt to verify no damage.

You could try bypassing the input board and bring +24 to directly to the pressure switch and see if this eliminates the alarm.
Reply With Quote

  #8   Ban this user!
Old 04-01-2011, 12:44 PM
 
Join Date: Mar 2011
Location: USA
Posts: 7
Industrial Tool is on a distinguished road

Well after a week with the flu, I'm finally back again. Removed the Input Board and there was a blown lead on the back. Already have a replacement in the machine, but now when I flip the main breaker in the back it wont power up. The drives at the bottom of the panel all start up but mothing else. I checked all of the fuses again and all were good. Also checked the powersuplies and they were good as well. Anyone else have this problem??
Reply With Quote

  #9   Ban this user!
Old 04-01-2011, 02:32 PM
 
Join Date: Mar 2011
Location: USA
Posts: 88
maver1ck is on a distinguished road
Buy me a Beer?

When you say "it won't power up" I'm assuming you mean the control doesn't come on. If so, I believe the relay to pull in the 110V is 24V coming through the I/O board you just replaced.

Since you indicated you have already checked the 24V power supply, since the board was just replaced, I would start by double checking all connections and wires to this board to make sure they are all seated well and where they are supposed to be.

If everything looks good, check at the green power button on the OSA to see if the power is making it there. This will at least let you know which side of the power button the problem is on.
Reply With Quote

  #10   Ban this user!
Old 04-01-2011, 03:01 PM
 
Join Date: Mar 2011
Location: USA
Posts: 7
Industrial Tool is on a distinguished road

It's more than just the control that wont power up. The red LED's on the communication board wont light up as they normally do. As a test I replaced the 110V Power supply that is next to the 24V Power supply from a working machine. Still nothing. I removed the new board to inspect it again and all leads look good. I checked each of the connections at the bottom of the as I re-installed them. All seated with no problems. All of the plugs are seated nicely to the new board as well.
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 04-02-2011, 11:47 PM
 
Join Date: Mar 2011
Location: USA
Posts: 7
Industrial Tool is on a distinguished road

Ok new news. I checked the new 24V Power Supply, only 1.2V to earth rail. Completely inspected every inch of 405 to fuse and 424 to all components, no frays or burns.

I unhooked everything from 424, checked power supply 23.8V. Started hooking up components one at a time and checking voltage.

Everything checked good until I hooked up the "new" input board (part# 1269581 rev E Serial 1070). Voltage dropped to 1.2V. With the input board out of the circuit I show 23.8V at all connections.

Luckily I had taken pictures of the old board for reference and all wires/plugs are in the correct places. Before installation of the "new" board, I placed it beside the old one and carefully inspected/compared the two. They were identical, except for the blown lead on the back of the old one.

Any ideas on what could drop the voltage from 23.8V to 1.2V when the input board is hooked up?
Reply With Quote

  #12   Ban this user!
Old 04-04-2011, 12:25 AM
 
Join Date: Mar 2011
Location: USA
Posts: 7
Industrial Tool is on a distinguished road

The connection in question is wire 424 to TB1-1 on the Input Board. I looked at both sides of the board to see where the circuit goes and didn't see anything coming out of the rail. What all does TB1-1 feed 24V to on this board?
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Arrow 1000 W/Acramatic 2100 - PC crashing Heinster Cincinnati CNC 3 02-11-2011 03:57 PM
Arrow 750 Acramatic 2100 Internal Error 0X80016 laka Cincinnati CNC 4 06-07-2010 08:32 AM
Arrow 500 - Acramatic 2100 No Power to Controller hodge_thomas Cincinnati CNC 2 05-10-2010 07:36 AM
Cinci Arrow w/2100 Siemens 611 error cnccalgary Cincinnati CNC 2 09-28-2009 04:29 PM
Acramatic 2100 Arrow 1000 need help griz-shop Cincinnati CNC 17 12-06-2008 12:49 PM




All times are GMT -5. The time now is 12:19 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361