V2XT: Spindle Enable dead fault.

Hey group. I'm having an on going problem with my unit that I'm unable
to figure out.

First some info: 1999 V2XT DX32 unit. completely original and being
run with 3 ph power VIA 3hp Hitachi VFD.

Unit powers up no problem, all axes home smoothly. I can jog and
locate the table just fine. The issue starts when I try to enable the
spindle.
The VFD (drive) registers current over load and trips out the safety
(like a braker would do) no damage is done.

So in an effort to source the overload here is what I've done so far.
I started with checking continuity on all the "enable" "start" "hi"
"lo" momentary switches and harness. All checked out normal. no dead
shorts to each other, no dead shorts to the chassis.

I then disconnected the leads to the motor itself and did the same
continuity test to all three leads (L1-L2-L3) with normal readings
(this was done with both ends disconnected from the machine checking
cross shorts and dead shorts)

So in an effort to remove the "Is-the-motor-fried" variable I then
powered it (the motor) up via direct feed from the VFD (controlling
start / stop / accel via the vfd control panel) This proved the motor
sound and smooth and the spindle not seized.

FINALLY I then powered up the mill with the motor left disconnected.
The enable procedure went fine with the screen showing "spindle HI"
Not soon after I notice the familiar smell of starting to melt / burn
wire or electrical component (that smell we all dread, secondly only
the seeing the "magic smoke" let out)

any suggestions why the vfd would dead fault only when the motor is
connected and where should I continue to hunt for my issue? Any
possibility the contactors are stuck closed? Can they be cleaned like
an electrical fuel pump contactor?

I'd be deeply in debt to any one that kicks me in the right direction.

Peace
__________________
9 1/2
B.C.I.T. Machinist CNC
Reply With Quote

  #2   Ban this user!
Old 03-22-2008, 02:51 PM
9 1/2's Avatar  
Join Date: Jan 2007
Location: PRIVATE
Posts: 129
9 1/2 is on a distinguished road

update:

I've been looking at the params on the Hitachi, SJ-200 nfu22, and tuned the amperage overload settings. I set it all the way up to 120% of drive rating (max. allowable) and still had an issue. It was then I realized the combined amperage draw of the V2XT machine was 20a and the most my drive will output is 12 amps (at120% over amp setting)
This leads me to believe the total draw is too much for the drive.
To that end I've been considering splitting out the two 120 volt legs that feed the two transformers. This way the VFD will only provide power when the spindle is called up, otherwise the rest of the system will run off 120 volt single phase power.

I've studied the schematics for a few days now (in anticipation of this issue) and feel this is my best option (rather than buying a THIRD larger vfd drive)

The transformers are taking two legs off the 3 phase power and converting it BACK to single phase 120 volts [1L1 plus 1L2 and 1L1 plus 1L3 respectively] (for the pc functions) and 100 volts DC (among other voltages like 24v etc etc) for the axis drive and motors.

does this seem like a reasonable approach?

Owen
__________________
9 1/2
B.C.I.T. Machinist CNC
Reply With Quote

  #3   Ban this user!
Old 03-22-2008, 05:00 PM
9 1/2's Avatar  
Join Date: Jan 2007
Location: PRIVATE
Posts: 129
9 1/2 is on a distinguished road

Well I sucsessfully split out the 120 volt components by inputing 240 volt single phase power to the T1 and T2 transformers. In turn they did what ever it is they need to do allowing the drives and pc to power up and enable.

I then turned on the VFD to provide 3 phase power to the spindle contactor blocks.

Enabled the spindle and every thing worked out fine. For a while ............ then three filters located on the input side of the spindle contactor blocks began to smoke. I powered the unit down and consulted the schematic.

Does anyone the purpose of these units? do they act like a regulator to remove excess amperage? I am puzzled and so close to my goal.
__________________
9 1/2
B.C.I.T. Machinist CNC
Reply With Quote

  #4  
Old 03-22-2008, 05:15 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,536
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by 9 1/2 View Post


FINALLY I then powered up the mill with the motor left disconnected.
The enable procedure went fine with the screen showing "spindle HI"
Not soon after I notice the familiar smell of starting to melt / burn
wire or electrical component (that smell we all dread, secondly only
the seeing the "magic smoke" let out)
I read through your posts a few times to try and get the gist of what is going on, If you have smoke/smell with the motor disconnected then you have a problem with the drive, I would say, I assume you do not have anything connected in the way of a contactor etc between the VFD and the motor?
You have 1 phase coming in to this machine? And the VFD is fed with 220~240 1 phase?
Normally it is hard to fry a VFD as it should go into current limit or shut down if short or ground problem.
Where is the spindle contactor wired in that you mention? If there is an input reactor, this is a 3 phase choke with three windings in series with each input phase, if three phase input.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 03-22-2008, 06:00 PM
9 1/2's Avatar  
Join Date: Jan 2007
Location: PRIVATE
Posts: 129
9 1/2 is on a distinguished road

Hi Al,

The source of the smoke were (was?) three items marked as "FILTER" on the schematic. They are connected down in the cabinette where the spindle contactor block is on the input side.

I've managed, through internet research, to ascertain these units are a resistor and a .1uF capacitor in series. It is used to dampen the electrical noise generated by the contactor.

so I know *what* they are & what they are for but not why they are burning.

I've now tuned the VFD down to output no more than 7 amps, enough to run the spindle motor, as this is now the only purpose of the VFD but there was no change.
__________________
9 1/2
B.C.I.T. Machinist CNC
Reply With Quote

Sponsored Links
  #6  
Old 03-22-2008, 11:10 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,536
Al_The_Man is on a distinguished road
Buy me a Beer?

Normally these would burn out if the voltage was exceeded either by input voltage high or a high prevalence of voltage spikes.
If they are indeed RC snubber's http://cnczone.com/forums/showthread...hlight=snubber
MOV's (voltage dependent resistors) are sometimes used in this application also,
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #7   Ban this user!
Old 03-24-2008, 09:57 AM
Ranchero50's Avatar  
Join Date: Feb 2008
Location: USA
Posts: 22
Ranchero50 is on a distinguished road

From experience, VFD's put out some serious spikes and weird voltages (seen over 600vdc on a 480 VFD output. Methinks without the motor hooked up the VFD output signal is running wild. Sounds like the filters are overwhelmed. I would recommend getting a rotory phase converter. My 308 draws 8.7A at idle feeding the converter.

Jamie
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
V2XT drive fault detected DF-ENTERPRISES Bridgeport and Hardinge Mills 5 03-28-2010 08:10 PM
Sweo spindle drive? new mill dead spindle Shizzlemah Fadal 13 12-18-2008 11:11 AM
V2XT error message "DRIVE FAULT detected (0,z,y,x) check log" rfdoyle Bridgeport and Hardinge Mills 4 10-08-2007 03:35 PM
Spindle enable alarm Fanuc OTB hien100881 General CNC (Mill and Lathe) Control Software (NC) 3 01-21-2007 01:29 AM
Hot Spindle on V2XT Bridgeport Spin Bridgeport and Hardinge Mills 5 10-14-2005 05:59 PM




All times are GMT -5. The time now is 12:12 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361