240v supply and 208v motor

I have a question about connecting service to a bridgeport cnc mill.I have 120/240 single phase service from power company running through a 5HP phaseamatic rotary converter and want to connect to a 208 volt machine.I see that the transformers can be wired for 230 volts .What else needs attention? Motor? Motor contactors?Motor overload heaters?I thank You for any info that could be provided.I just registered onto this site recently and have been reading and learning from all the threads and responses.
Reply With Quote

  #2  
Old 11-23-2007, 11:55 PM
mxtras's Avatar
Silver Member
 
Join Date: May 2005
Location: USA
Age: 45
Posts: 1,810
mxtras is on a distinguished road

I am not clear on what you are asking. What's this about a transformer?

Running a 208V motor on 230-244V is not a problem but it sounds like you might also be looking to run a complete machine - including a processor??

Scott
__________________
Consistency is a good thing....unless you're consistently an idiot.
Reply With Quote

  #3  
Old 11-24-2007, 10:14 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,536
Al_The_Man is on a distinguished road
Buy me a Beer?

I don't think you would need to worry going from 208 to 240, It is not quite as drastic as going from 440 to 220, where wiring gauge and O/L heaters would maybe need to be changed.
A 208 device will draw slightly more on 240, but wire & O/L's are usually rated quite a % higher.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #4   Ban this user!
Old 11-24-2007, 02:14 PM
 
Join Date: Nov 2007
Location: USA
Posts: 7
isu19151@verizo is on a distinguished road
240v supply and 208v motor

Scott and Al the Man thank You for your reply.I am looking to connect the mill to a 230v 3 phase line after it goes through a rotary phase converter.The transformers are in power distribution enclosure and supply power (110-120vac)to all systems except spindle motor.Jim
Reply With Quote

  #5   Ban this user!
Old 11-28-2007, 02:34 AM
 
Join Date: Oct 2006
Location: usa
Posts: 36
awright is on a distinguished road

I'm no motor expert, but I'd be very cautious about applying 240 volts to a 208 volt motor. That's a 15% overvoltage and you could run into magnetic saturation of the motor stator laminations. If saturation does occur, you can get very high peak currents.

If the motor manufacturer can be contacted, consider calling them to ask about overvoltage tolerance. Or just ask any motor manufacturer.

At the very least, when you power the motor up on 240 volts, listen carefully for excessive hum and watch for any signs of excessive current. If things sound normal, measure current in each phase, turning the motor off between measurements. If measured currents under load are not more than 15% above rated current, I guess it would be reasonable to proceed cautiously.

It's a little cumbersome, but one available and easy method of reducing the voltage applied to the motor is to use a separate 240 volt to 36 volt transformer to reduce the voltage applied to each winding. The low-voltage winding of the transformer only needs to have a current rating equal to the rated current of the motor under load. The primary is connected across the 240 volt supply to the winding and the secondary is connected in series BUCKING with the motor winding. This reduces the voltage applied to the motor by an amount equal to the secondary voltage of the transformer.

36 volt transformers are pretty rare, but 24 volt transformers are very common on surplus. If it was my machine, I'd feel better reducing the voltage applied to the motor, even by 24 volts.

awright
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 11-28-2007, 06:59 AM
gus gus is offline
 
Join Date: Jan 2005
Location: us
Posts: 878
gus is on a distinguished road

most motors are rated 208/230

it is rare that 240 is over 240, but sometimes it can be, that is the only time I would be concerned
Reply With Quote

  #7  
Old 11-28-2007, 08:05 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,536
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by awright View Post
I'm no motor expert, but I'd be very cautious about applying 240 volts to a 208 volt motor. That's a 15% overvoltage and you could run into magnetic saturation of the motor stator laminations. If saturation does occur, you can get very high peak currents.
I am not sure magnetic saturation would occur and be retained, this is an AC current being dealt not DC, also the common inrush current in an AC motor exceeds 10 times the normal running current every time it is started, decreasing with rpm. This is increased by the shorted turn effect of Armature conductor bars.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #8   Ban this user!
Old 11-28-2007, 06:19 PM
 
Join Date: Nov 2007
Location: USA
Posts: 7
isu19151@verizo is on a distinguished road
240v supply and 208v motor

Thank You for your response.I have reconfigured the transformers for 230-240v input and now am thinking about adding a 3 phase line monitor as added protection for the 208v motor.According to the description it will balance the phases at 2-4-6-8 or 10 % per a selector switch.I was also thinking that it would keep the DC voltage in the drive and controller circuit within specs if the AC voltage was as it should be then DC voltage would be also.???? Any Thoughts.Jim
Reply With Quote

  #9   Ban this user!
Old 11-29-2007, 01:23 AM
 
Join Date: Oct 2006
Location: usa
Posts: 36
awright is on a distinguished road

I'm trying to understand what you are describing regading the 3 phase line monitor. It sounds like you believe that the monitor will influence and control the phase balance. If it is what I have seen as line monitors, I believe that what it will do is give an alarm if the phase balance exceeds the setting you have selected. It will not do anything to modify or control the phase balance.

Still a good idea, but since they are primarily intended to monitor solid three phase lines coming in from the utility, the balance of which may be influenced by the loads placed on the various phases throughout the plant, I fear that the softer and erratic phases supplied by a phase converter may give you alarms fairly regularly to the point that you ignore it or disconnect it. Have you heard from other users of phase converters that phase monitors are useful?

Don't forget that two phases are being supplied directly from the line, but the third is being artificially generated by the idler motor ond the run capacitors. That third phase is pretty squirrilly and subject to fluctuation with loading, depending upon the size and design of the phase converter.

awright

I also do not believe that a phase monitor will do anything to maintain your DC voltage at a desired level.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bosch Router GMF1400 Question (European 240V) RASPNC DIY-CNC Router Table Machines 9 01-01-2012 06:07 PM
Bosch Axis Drive Board Z15-1-240V RMARCH Bridgeport and Hardinge Mills 0 08-15-2007 12:35 PM
240V Deckel DE20 Sinker EDM for sale dpriebe General Metal Working Machines 0 12-18-2006 12:23 PM
208V 3ph machine on 240V 3ph? DennisCNC General Electronics Discussion 2 11-21-2006 06:34 PM
Can the motor be re-wired to opperate from 240V 3ph Ken_Shea General Electronics Discussion 6 09-12-2005 09:12 PM




All times are GMT -5. The time now is 12:04 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361 362 363 364 365 366 367 368 369 370 371 372 373 374 375 376 377 378 379 380 381 382 383 384 385 386 387 388 389 390 391 392 393 394 395 396 397 398 399 400 401 402 403 404 405 406 407 408 409 410 411 412 413 414 415 416 417 418 419 420 421 422 423 424 425 426 427 428 429 430 431 432 433 434 435 436 437 438 439 440 441 442 443 444 445 446 447 448 449 450 451 452 453 454 455 456 457 458 459 460 461 462 463 464 465 466 467 468 469 470 471 472 473 474 475 476 477 478 479 480 481 482 483 484 485 486 487 488 489 490 491 492 493 494 495 496 497 498 499 500 501 502 503 504 505 506 507 508 509 510 511 512 513 514 515 516 517 518 519 520 521 522 523 524 525 526 527 528 529 530 531 532 533 534 535 536 537 538 539 540 541 542 543 544 545 546 547 548 549 550 551 552 553 554 555 556 557 558 559 560 561 562 563 564 565 566 567 568 569 570 571 572 573 574 575 576 577 578 579 580 581 582 583 584 585 586 587 588 589 590 591 592 593 594 595 596 597 598 599 600 601 602 603 604 605 606 607 608 609 610 611 612 613 614 615 616 617 618 619 620 621 622 623 624 625 626 627 628 629 630 631 632 633 634 635 636 637 638 639 640 641 642 643 644 645 646 647 648 649 650 651 652 653 654 655 656 657 658 659 660 661 662 663 664 665 666 667 668 669 670 671 672 673 674 675 676 677 678 679 680 681 682 683 684 685 686 687 688 689 690 691 692 693 694 695 696 697 698 699 700 701 702 703 704 705 706 707 708 709 710