    Converting Bridgeport 408v to 208v?

    I have a line on a used Bridgeport Series II for sale we might wanna pick up.

    It's wired for 408v 3-ph. We don't have that, nor are we likely to get 408v service. We have 208v 3-ph.

    Is the Series II possible to rewire into a 208v 3ph configuration?

    I do not know how many HP this one is. I see that some Series II are 2hp, some are 4hp. It is practical to simply replace the motor with a 208v 3ph? If some Series II are 2hp, then even if it's got a 4hp on it now, a 2hp would still be appropriate for what it does, wouldn't it?

    Is it always that 408v Series II is going to be 4hp? Seems like there's not a lot of reason to go with such a high voltage for a 2hp drive.

    The seller has said the control for feed gears does not work. I'm not clear on what kind of failure that is. Is there some common thing that breaks on the Bridgeport Series II which this might be? This mill has the Acu-Rite head on it, could this be an Acu-Rite problem? How pricey would it be to replace the parts?
    Last edited by MechanoMan; 10-20-2011 at 05:06 AM.


  2. #2
    Moderator
    Join Date
    Nov 2004
    Location
    USA
    Posts
    2,986
    Downloads
    0
    Uploads
    0
    Sounds like a S2STD. If so it is 4HP and the motor can be rewired for 220V. There usually is a transformer for control voltage than also can be reconfigured.
    The downfeed is a electronic motor unit and probably the board is shot. But there is a small micro switch on top of the quill that sometimes gets its wires cut that could be part of the problem.

    George
    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)


  3. #3
    Registered
    Join Date
    Jul 2011
    Location
    USA
    Posts
    18
    Downloads
    0
    Uploads
    0

    Cool

    I had a similar problem years ago with a R2E3 we had. It was wired for 208V and we were running 240V.

    It kept blowing drive fuses. On a BPT techs advise, we used 2 BUCK/BOOSTING transformers. Solved the problem until we ran the precision out of the machine 10 years later. In my case we BUCKED the power down to 208V. In your case you will BOOST the power to 408V. This is the best way to handle this situation.

    I WOULD NOT, try to change the machine wiring. Purchase 2 BUCK/BOOSTING transformers from your local electric supply house. If you can follow a wiring diagram you can wire this tranformer to make the 408. It will be in the area of 30 or so connections you will have to make. between the two transformers. Make up a 3/4" plywood mounting board (ala like an electriction does for a circuit panel.) And use 3/4" EMT to connect the transformers together. Hang on the wall behind the machine. Make all the connections EXCEPT the leads going to the machine. Leave these hanging out in space all isolated. Energize the Transformers. Take your multi tester and check to see you have 408 V (+/- 10%) coming out between any two hot wires. Now you are good to go. De-energize and hook up leads to machine. Opon fire up, quickly check the coolant pump to see if it pumps coolant out. If it does not, switch any one hot wire at the machine to reverse the polariity to the correct direction.

    If you can't handle the BUCK/BOOST wiring. Have an Electrician make it for you in his shop. 10 years after making mine, a local shop bought mine for $350.00. So, they are valuable even when you lose the need for use.

    One other tip: If you go this route, use the breaker that shuts off power to the Tranformer for the Machine power disconnect switch. This way, you are not transforming power 24/7 365. Only when machine is in use.

    Jake


  4. #4
    Moderator
    Join Date
    Nov 2004
    Location
    USA
    Posts
    2,986
    Downloads
    0
    Uploads
    0
    Re reading this is it a 408 or 480 volt machine?
    Buck boost are good for going about 10 percent or so.
    May be a non USA machine. May need a matching transformer.

    George
    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)


  • #5
    Registered
    Join Date
    Jul 2011
    Location
    USA
    Posts
    18
    Downloads
    0
    Uploads
    0
    Yes. +/- 10% is correct. But I clearly remember the Magnatek Transformers I bought could be wired for many standard and non-standard volts. This way you could wire the Transformers to the exact volts or to within 10% of where you needed to be. Now, if it's a 50HZ machine....that's another problem.

    Jake


  • Similar Threads

    1. 220V/208V?
      By vpmachine in forum General Metal Working Machines
      Replies: 2
      Last Post: 01-28-2011, 01:54 AM
    2. Need Help!- VF5 208V conversion?
      By machinist007 in forum Haas Mills
      Replies: 2
      Last Post: 08-04-2010, 08:18 PM
    3. New Machine Build- Couple of questions on converting a bridgeport to cnc
      By jawsoflife in forum Bridgeport and Hardinge Mills
      Replies: 3
      Last Post: 03-09-2008, 08:31 AM
    4. 240v supply and 208v motor
      By isu19151@verizo in forum Bridgeport and Hardinge Mills
      Replies: 8
      Last Post: 11-29-2007, 02:23 AM
    5. 208V 3ph machine on 240V 3ph?
      By DennisCNC in forum General Electronics Discussion
      Replies: 2
      Last Post: 11-21-2006, 07:34 PM

    Posting Permissions


     


    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.