I have my tc-22 finally back close to running with a fresh harddrive,dos install and software install and reman bmdc . I have one problem . When I enable my drives the z axis brake release and the axis drops untill e-stop is hit, I blocked up the axis and now I can enable the drives but when i hit 8 to home the axis I get a message that GAURDS NOT IN PLACE save to error file then I get HOME FAILED I only get the gaurds message whem i try to home so believe it has something to do with each other. Are the gaurds actually a protective gaurd or a safety (gaurd) in the control? If I watch the maint page I can look at all the parameters and can see the state change when I push the buttons on the machine like tool eject etc Last edited by tpmx57; 06-20-2011 at 07:53 PM. |
|
#2
| |||
| |||
| Figured out the guards error I am getting. It means the safetys are enabled in the control and wont home axis or do much with the door on the enclosure open. I found this in the manual but cant find how to disable the door interlocks in the control. Is this possible? |
|
#3
| |||
| |||
| If I remember right there is a parameter for it. The maintenance page should give a list of parameters and also display a description for the parameters. |
|
#5
| |||
| |||
| een chasing this z axis problem with no luck. Can someone advice me as to what proceedure to use to troubleshoot this? When I enable my drives my z axis will drop all the way to thr table if not for e-stop. If I block up the z axis I can enable the drives but within a short time the control will fault out with a z axis drive overcurrent. If I enable the drives and right away press home the tool carousel will home but then the z axis drive fault will occure. i checked the drives and have the correct power to those. I checked the 5v to the auf board and have correct voltage there. Would the problem be encoder problems or a bad drive problem? My machine has the Parvex motor so was hesitant to swap drives. The control is seeing logic from pushbuttons but as from the encoders i am no sure. If I am on the maint page I enable the drives and when the brake releases I try turning the ballcsrew and dont see movement on the readouts then the control faults out. Not sure if thr control will show any movement on the readouts at that time or not. Also the readout shows the z axis being at exactly -9.000. The chances of the acis being blocked at exacly that spot would be really small. This leads me to think the prblem is in the encoder circuit, But wouldnt explain the drive overcurrent. Thanks for the insght i |
| Sponsored Links |
|
#6
| |||
| |||
| tpmx57 Your Auf board voltage has nothing to do with your drive voltage You have to check the ribbon cables that go from the piggy back board to the drives, you need to have the 5 volts there on each cable, you have it on the X & Y or they would not be working, Do you have the ribbon cable for the Z axes on the right plug coming off the piggy back board, the piggy back board has a plug for the fourth axes, you can not use this for the Z axes, If you don't have voltage at the ribbon cable to the BMDC board, first check the ribbon cable if the cable is ok then you most likely still have a BMDC Board Problem You need to check the wiring print as to which pins to check on the ribbon cable for the 5 volts
__________________ Mactec54 |
|
#7
| |||
| |||
| I guess I didnt explain it correctly. I have the correct voltage at the drives which I dont remember exacly off hand but think it was 144 volts I would have to check the manual again but was within the tolerance the manual gave. I also checked to make sure the auf board had 5 volts where it should,it was fine. The bmdc loads correctly and the cables are plugged in to the correct spots. I believe the furthest from the door is the A drive. I didnt check the cables from the piggyback board to the drives but now I will. What would cause a z axis drive overcurrent fault? Possibly a faulty piggyback board ?Have read much about these going bad. |
|
#8
| |||
| |||
| 1) Since the Z axis has not homed yet what the position says on the read out doesn't mean anything 2) The z axis is either running away or free falling when the brake releases. Since you get an over current alarm when you block the z axis up I would suspect it is running away giving you an over current as it pushes against your block. Another possibility is that the power cable to the motor is bad and shorting out. This would prevent power from getting to the motor allowing it to free fall and still allow the drive to go into over current. Disconnect the motor leads from the drive and from the motor and check the cable for shorts and opens. If you have a megger available with the cable hooked to the motor but not to the drive meg out the motor and cable to make sure everything is good. With the motor unhooked from the drive and the z Axis blocked up enable the drives. Can you measure output voltage coming from the drive? (If you still get an over current alarm I would suspect the drive is bad) Are you getting a signal to the drive telling it to move? Has anything been changed with the Z axis motor and drive? Is it possible the power leads were reversed or the tachogenerator leads were reversed? (Note if you replaced either of these it is possible the new parts are not wired the same as the original as Bridgeport did not wire every machine the same) |
|
#10
| |||
| |||
| I was in the maint page on the tc-22 today just to check some parameters and am curious to why no parameter matches the manual I was looking at parameter041-042-043 the manual shows them to be 00000000192,00000000192 and 00000000224 for the z axis this is the Axis Applied Motor Voltage for x,y and z The control shows 14.00000000,14.00000000 and 16.00000000 for z. is this correct? No parameter matches the manual so I assume the control makes a conversion and thats what I see Can someone explain what I see? |
| Sponsored Links |
|
#11
| |||
| |||
Where did you get the parameters you loaded when you installed the new hard drive? Also is it the same version of software that you had on it before? |
|
#12
| |||
| |||
| When I I installed the harddrive I copied the bmdcprms.sys file from the old harddrive to the new after loading the software. I will have to boot the machine andsee what version the software is. My manual has all the parameters listed and an explanation but none are the same as when I check them on the maint page at the machine Confused about this |
![]() |