    Recommend Fuse rating for Kelinginc KL- 7212

    I like to add an fuse to the power supply.

    Any Fuse rating recommendations for Kelinginc KL- 7212 powersupply? Note I'll be using 120vac.

    KL- 7212 powersupply spec, unregulated Power Supply 860W, 72VDC/12A, Single Rectifier Module,120VAC or 230VAC.

    Thanks.


  2. #2
    Registered
    Join Date
    Dec 2005
    Location
    UK
    Posts
    74
    Downloads
    0
    Uploads
    0
    Hello

    I assume you mean a fuse on the input side. That given, the fuse needs to be larger than
    860 (watts) / 120v (your input volts) which gives 7.2 Amps. Most power supplies take more current at switch on ( known as inrush current) and also you do not want the fuse to blow regularly. I would fit an 8 Amp Slo-blow fuse (if you can get them) or a 10 normal fuse.

    A Slo-Blow fuse will not blow for several seconds at start up even if the current is several times the rating but will blow in several minutes if current is taken at the rated current. Similar to a thermal trip which you mich also like to check out.

    I hope this helps

    Richard


  3. #3
    Registered spaceballs_3000's Avatar
    Join Date
    Apr 2008
    Location
    USA
    Posts
    46
    Downloads
    0
    Uploads
    0
    Quote Originally Posted by rgammage View Post
    Hello

    I assume you mean a fuse on the input side. That given, the fuse needs to be larger than
    860 (watts) / 120v (your input volts) which gives 7.2 Amps. Most power supplies take more current at switch on ( known as inrush current) and also you do not want the fuse to blow regularly. I would fit an 8 Amp Slo-blow fuse (if you can get them) or a 10 normal fuse.

    A Slo-Blow fuse will not blow for several seconds at start up even if the current is several times the rating but will blow in several minutes if current is taken at the rated current. Similar to a thermal trip which you mich also like to check out.

    I hope this helps

    Richard
    That give me a good idea of what I need to do now.
    Thanks Richard!


Similar Threads

  1. KelingInc, you are the best.
    By alexccmeister in forum Vendor Discussion
    Replies: 4
    Last Post: 01-19-2009, 11:39 PM
  2. KelingInc and Mach3 trouble
    By Normann in forum Automation Technology Products
    Replies: 9
    Last Post: 09-26-2008, 11:12 PM
  3. Newbie- Kelinginc for steppers and controller
    By haku in forum DIY CNC Router Table Machines
    Replies: 2
    Last Post: 04-18-2008, 01:10 PM
  4. Kelinginc question
    By lovebugjunkie in forum Commercial CNC Wood Routers
    Replies: 2
    Last Post: 08-11-2007, 03:00 PM

Posting Permissions



About CNCzone.com

    We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

Follow us on

Facebook Dribbble RSS Feed


Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.