    Information needed on new power supply

    I received the g540, steppers and power supply today and it came with zero documentation. I was able to go to the web site and download the limited information available. I got answer's for my stepper questions but I still need additional information on the power supply. Please explain the purpose of the following terminal numbers 4, 5, 6, 7, 8 and 15



  2. #2
    Registered KOC62's Avatar
    Join Date
    Mar 2009
    Location
    Canada
    Posts
    276
    Downloads
    0
    Uploads
    0
    Here is my guess.

    Pins 4 & 5 are not used, hence no connection (N.C)
    Pins 6, 7 are most likely used for romote on/off. If not used a jumper would be connected between pins 6 & 7.

    Pins 8 & 15 are sense lines.
    May be used in case there is too much voltage drop to your load. If you can drive a load without the use of Pins 8 & 15 then you don't need to connect anything to it.

    This link may help... http://www.power-factor-1st.com/uplo...oting-tips.pdf

    You didn't say what power supply you were using so I couldn't look for it.


  3. #3
    Registered doorknob's Avatar
    Join Date
    Jan 2010
    Location
    USA
    Posts
    1,733
    Downloads
    0
    Uploads
    0
    [edit: I didn't see the reply by KOC62 before posting]

    My best guess:

    4, 5 NC - means "not connected" or "no connection" (ignore those terminals)

    6 R.C.G - Remote control terminal

    7 R.C. - Remote control terminal

    8 +S - remote positive voltage sensing terminal

    15 -S - remote negative voltage sensing terminal

    The remote control terminals are supposedly for adding a (low-voltage) switch to turn the supply on and off.

    The sense terminals allow the voltage actually applied to the load to be regulated, instead of regulating the voltage at the power supply itself.

    There is a discussion of those terminals at http://www.cnczone.com/forums/diy-cn...w_voltage.html along with a link to documentation, although the poster(s) reported difficulty in making the remote function work.

    My suggestion would be to ignore all of those terminals for now.


  4. #4
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,939
    Downloads
    0
    Uploads
    0
    In most P.Supplies with remote, the +S/-S has to be connected to the DC output +- respectively if not using the remote sense wiring.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #5
    Registered doorknob's Avatar
    Join Date
    Jan 2010
    Location
    USA
    Posts
    1,733
    Downloads
    0
    Uploads
    0
    Quote Originally Posted by Al_The_Man View Post
    In most P.Supplies with remote, the +S/-S has to be connected to the DC output +- respectively if not using the remote sense wiring.
    Al.
    Don't they typically come already jumpered?

    I suppose that it depends on the particular supply and vendor.


  • #6
    Registered IBBruin's Avatar
    Join Date
    Jan 2012
    Location
    USA
    Posts
    103
    Downloads
    0
    Uploads
    0
    Quote Originally Posted by KOC62 View Post

    You didn't say what power supply you were using so I couldn't look for it.
    Sorry, 48V 10A I was hoping the supplier would provide exact documentation so I posted in the supplier section of where I purchased it.

    I could have done a better job in describing the supply so here it is.
    Attached Thumbnails Attached Thumbnails Information needed on new power supply-ps.jpg  


  • #7
    Registered KOC62's Avatar
    Join Date
    Mar 2009
    Location
    Canada
    Posts
    276
    Downloads
    0
    Uploads
    0
    Your picture looks to me that all the necessary jumpers are attached. You provide the AC power and are ready to connect the 48V to your load.


  • #8
    Registered doorknob's Avatar
    Join Date
    Jan 2010
    Location
    USA
    Posts
    1,733
    Downloads
    0
    Uploads
    0
    That photo is indeed worth 1000 words.

    The R.C. terminal is shorted to the R.C.G. terminal.

    If you want to use a remote, low-voltage power switch, remove the jumper between those terminals and instead wire those terminals to a normally-open switch.

    If you would like remote sensing of the voltage (at the load), remove the jumpers between the S+ and V+ terminals and between the S- and V- terminals, and then wire the S+ to the positive terminal at the load, and wire the S- terminal to the negative terminal at the load.

    But, you should still be able to use it without changing any of those jumper settings.


  • #9
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,939
    Downloads
    0
    Uploads
    0
    Quote Originally Posted by doorknob View Post
    Don't they typically come already jumpered?

    .
    The Hammond and the other linear regulated that I use do not come jumpered.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #10
    Registered KOC62's Avatar
    Join Date
    Mar 2009
    Location
    Canada
    Posts
    276
    Downloads
    0
    Uploads
    0
    Only in Canada, eh?


  • #11
    Registered IBBruin's Avatar
    Join Date
    Jan 2012
    Location
    USA
    Posts
    103
    Downloads
    0
    Uploads
    0
    I got all that hooked up, all I can say is WOW.

    I've never seen my router move that fast in the last 8 or so years I've had it. I had to slow it down to 50 ipm's or it would run out of work surface before it got finished accelerating! I'll post a video in another thread. Anyone reading this and still fooling with the chinese junk, do yourself a favor and throw that junk as far as you can. I've wasted more $$ in materials than the price of my new electronic setup due to missed steps.

    I guess WOW isn't all I had to say after all.


  • Similar Threads

    1. '98 VF2 Low Volt power supply source needed
      By LakesideMachine in forum Haas Mills
      Replies: 0
      Last Post: 01-10-2011, 11:48 AM
    2. power supply needed.... please help
      By goneflyin in forum General Electronics Discussion
      Replies: 8
      Last Post: 01-09-2010, 11:49 AM
    3. Need Help!- Amp needed for 24V power supply for my CNC?
      By samim in forum General Electronics Discussion
      Replies: 0
      Last Post: 07-12-2009, 05:13 PM
    4. Power Supply help NEEDED QUICK
      By Cold Fusion in forum CNCzone Club House
      Replies: 3
      Last Post: 12-08-2005, 11:19 PM
    5. Power supply wiring help needed
      By DJ Morrow in forum General Electronics Discussion
      Replies: 1
      Last Post: 10-27-2005, 12:05 AM

    Posting Permissions


     


    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.