    Clarification on wiring KL7220 in 230V.

    I am wiring a KL7220, KL6520, & a KL3815. I am wiring them 230V. The schematic from Keling website states:
    "AC power connections:
    115Vac – 2 red wires to neutral & 2 black wires to
    hot. 220Vac – 1st red wire to neutral, 1st black wire to
    2nd red wire, and the 2nd black wire to hot."

    In 230V ac, there are two 115V legs and a ground (no neutral wire). I assume that "1st red wire to neutral" means 1st red wire to 1 leg of 115V. and the "2nd black wire to hot" means to the second leg of 115V. There is no connection to AC power ground from the KL7220. Please confirm or correct this assumption.

    Also, should the chassis of the KL7220 be connected to the AC power ground?

    Thanks for any help.
    --Mike


  2. #2
    Registered
    Join Date
    Aug 2006
    Location
    United States
    Posts
    71
    Downloads
    0
    Uploads
    0
    Did you ever get an answer to this?

    I am also trying to make sure I wire the same power supplies correctly.


  3. #3
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,938
    Downloads
    0
    Uploads
    0
    If using 240vac the primaries are in series use 240v 1ph only, forget about neutral, You also should take an earth ground to the frame of the power supply, I have found R.O.C. equipment very lacking as to providing ground and safety.
    You also have the option of parallel primary for 120v 1 ph.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  4. #4
    Registered
    Join Date
    Aug 2006
    Location
    United States
    Posts
    71
    Downloads
    0
    Uploads
    0
    Al! You are everywhere!

    Here is what I am having trouble with. See Picture.

    These are the instructions for the wiring:

    "1st red for neutral, 1st black to 2nd red,
    and the 2nd black to hot wire."

    So in my picture I am seeing this as:

    Number 1 (Black): L1 (230VAC)
    Number 2 (Red): Connect together with wire #3
    Number 3 (Black): Connect together with wire #2
    Number 4 (Red): Neutral (or in my case L2 (230VAC)

    And I have the panel that they are mounted to grounded to a ground bar that my main system is grounded to, coming from my disconnect for the power.

    Seem right?
    Attached Thumbnails Attached Thumbnails Clarification on wiring KL7220 in 230V.-img_0619.jpg  


  • #5
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,938
    Downloads
    0
    Uploads
    0
    That sounds correct, fortunately if you get it backwards with series winding, you just end up with no output.
    If you make a mistake with the 120v parallel connection you blow a fuse!.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #6
    Registered
    Join Date
    Aug 2006
    Location
    United States
    Posts
    71
    Downloads
    0
    Uploads
    0
    Thanks Al! I should be powering them up this weekend I hope.


  • Similar Threads

    1. Wiring Clarification
      By Lotusjohn in forum Granite Devices
      Replies: 3
      Last Post: 12-27-2010, 06:20 AM
    2. Need Help!- Need Help! 5HP motor 460V to 230V?!
      By diyengineer in forum General Electronics Discussion
      Replies: 22
      Last Post: 10-25-2010, 07:08 AM
    3. Rewiring Transformer for 230V Input
      By keebler303 in forum General Electronics Discussion
      Replies: 3
      Last Post: 05-27-2010, 12:24 PM
    4. I need 3Phase 230V off 1Phase 110V, can I get help?
      By idtkid in forum General Electronics Discussion
      Replies: 11
      Last Post: 07-14-2009, 09:56 AM
    5. Need help wiring 230V AC spindle motor
      By Heavy D in forum Knee Vertical Mills
      Replies: 4
      Last Post: 05-07-2006, 12:24 AM

    Posting Permissions


     


    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.