Hello, I am into my first retrofit and need some help. I plan to start a build thread and have been taking pictures, but I need to get my ducks in a row for that. The machine is a 1990-1992 Ram Mill 13x42 CNC vertical knee mill. This is my first "real" machine tool. It came with a Hust control which eventually lost all but MDI 1 step operation. After 2 years or so of shopping and reading, I finally purchased the Ajax/Mach3 setup for 3rd party drives. Scott at Ajax said he would take a look at the manual for my inverter to hopefully help me out with a diagram of how to connect it to the Ajax system. Well, 10 days later of 12 hour days working on the mill has put me way past the point where I would've liked to have had the answers I'm seeking. I bet this is a real simple thing for many of you. The inverter I have is a Mitsubishi A024 - 3.7K. I do not have the PU unit for it, so I cannot change parameters. I do have the manual for the inverter. Any help would be greatly appreciated!!! ![]() Thanks, Dave |
|
#2
| |||
| |||
| You will want to buy the keypad for it sooner rather than later. An inverter you can't program or troubleshoot is less than worthless. If for some reason that is impossible, you could replace it for about $350. How much is your time worth? That said, assuming yours is programmed in a more or less default configuration, you can probably just use the diagram in the manual (section 6.3 in the copy I found online): Close SD to STF to run forwards. Close SD to STR to run reverse. Close SD to RES to reset faults. Apply 0-10V analog speed reference to terminals 2 and 5 (analog output to 2, common to 5). The Fault output (wired to a PLC input so you can detect when the inverter faults) would use either A and C or B and C, depending on whether you want a normally-open or a normally-closed fault signal. You probably should use normally-closed, which is probably B and C. |
|
#3
| |||
| |||
| Thanks for the help! Some of that I did actually understand out of the manual, but the alarm contacts definitely threw me, and I wasn't positive about any of it. I'm hoping that I can run the inverter in the external control mode and not need to change parameters.There is also a "MRSAT" terminal on the inverter- would I use this to stop the spindle? I have mounted a maintained switch on my control panel for spindle on/off that I actually wired into a contactor feeding the 3 phase to the inverter. The control for this contactor also runs through the e-stop relay. I'm thinking maybe I should have the contactor controlled only by the e-stop and for normal spindle on/off operation, I should wire into that MRSAT terminal. Any thoughts on this? Also, I find the Ajax documentation lacking. There are conflicts on the pinouts and other needed info is just plain missing. Where on the Ajax GPIO4D do I wire these connections to the inverter??? I followed Scott's diagram to connect my AMC drives - that ate up input 13, which the documentation, I believe, says spindle enable, for instance??? I know I'm asking a lot of questions, but, hopefully, they are simple answers. ![]() Any additional help will also be appreciated! Thanks Again, Dave |
|
#4
| ||||
| ||||
| You definitely need a PU unit. Try ebay, is this one is a common one. ebay #330514218755 Al.
__________________ CNC, Mechatronics Integration and Machine Design. “Logic will get you from A to B. Imagination will take you everywhere.” Albert E. |
|
#5
| |||
| |||
| From the amount of times I've seen cncsnw and Al The Man post with awesome info, I know now I need the PU. I made an offer on one on feebay - didn't know if that FR-PU02E would work, manual lists the FR-PU03E, so that's the one I made the offer on. Thanks for the info. By the Way, Al The Man, I saved some info from a thread where you and others helped someone out with a differential to TTL converter chip and the pinout connections to connect an old style (like my Sumtak) MPG wheel to Ajax. I purchased the chip, a socket and a small board and soldered it all up and connected it last night. I have one question that will probably make you laugh, but how do you know the chip orientation? I got the data sheet on the IC from Digikey and I see the indent on the schematic that matches the socket, but the only thing on the IC is the lettering on top and a little indented circle on top. Which way is which? I got 2 IC's in case I blew one. |
| Sponsored Links |
|
#6
| ||||
| ||||
| Sometimes the identification is a bit obscure, the ones with the U in the centre of the end is usually more obvious. But the indented circle should be in one corner, the nearest pin is pin 1. Al.
__________________ CNC, Mechatronics Integration and Machine Design. “Logic will get you from A to B. Imagination will take you everywhere.” Albert E. |
|
#8
| |||
| |||
| I doubt you need to use the "MRSAT" terminal at all. You probably don't want or need additional panel switches or switch-controlled contactors. Let the CNC control start and stop the spindle for you. It will start and run the spindle by closing SD to either STR or STF, and keeping it closed for as long as the spindle is to remain running. It will stop the spindle by opening that connection. If you want a minimal level of E-stop protection, route the SD connection that comes from the inverter to the common point(s) of the PLC relays through a pole of your E-stop contactor. If you want a more robust level of E-stop protection (but one that is harder on your inverter) then route the 3-phase power that feeds the inverter either through the E-stop contactor, or through a separate contactor that is switched by the E-stop contactor. If you want additional front-panel buttons to start and stop the spindle, wire them to PLC input points and put logic in the PLC program to recognize them as manual-mode spindle start and stop. You can use any of the 16 relays on the GPIO4D board to command spindle run and reverse. Your PLC program is responsible for closing the correct relays when it wants the spindle to run. The most common default PLC programs I see for the GPIO4D have spindle run (either direction) on OUT7, and spindle reverse on OUT8. The wire from the SD terminal would go to the OUT7 common; you would install a jumper from the OUT7 output to the OUT8 common; the run-forward signal would go from OUT8 NC (normally-closed) to STF; and the run-reverse signal would go from OUT8 NO (normally-open) to STR. |
|
#9
| ||||
| ||||
| I am not sure about that particular model, I have use the A200 that has a MRS input, this is a stop input, I usually set mine up for either fwd or rev. So either on is on or off, so the MRS input function is not used. Al.
__________________ CNC, Mechatronics Integration and Machine Design. “Logic will get you from A to B. Imagination will take you everywhere.” Albert E. |
|
#10
| |||
| |||
| Al - Thanks Again, I'll explore that terminal's function a bit more. cncsnw - thanks very much - this is what I need. I am concerned with having a very limited number of inputs on the GPIO4D; that's why I was looking to have my panel switches control the spindle on/off outside of the GPIO4D. I currently have an e-stop relay (24VDC coil) which is controlling a 3 pole contactor feeding the 3 phase to the inverter. I read in the inverter manual that it was hard on the inverter, as you said to use the contactor, but it was vague about whether it was refering to the contactor on the line or on the load side of the inverter. That's when I read something about the stop terminal and thought maybe I could use that for manual spindle on/ off. The old controller had the on/off button and I like having it. As far as the robust e-stop...absolutely! I actually also have the estop relay controlling another contactor which will break the AC inputs to each of the 3 AMC drives. My thinking was that anything that can do harm is controlled by the e-stop. As far as the inputs go, maybe you would be kind enough to help me a little more. This is what I have for my inputs currently: in 1. limit x- in 2. limit x+ in 3. limit y- in 4. limit y+ 1-4 com. 24vdc common in 5. limit z- in 6. limit z+ in 7. (was thinking jog -) in 8. (was thinking jog +) 5-8 com. 24vdc common in 9. (was thinking cycle start) in 10. (was thinking feed hold) in 11. e-stop in 12. 9-12 com. in 13. x axis enable in 14. y axis enable in 15. z axis enable in 16. (should this be spindle fault?) 13-16 com. 5vdc+ I also have 2 selector switches: 1. axis select - x,y,z 2. multiplier - 1x,10,100x should the common of these switches go to 5vdc+ or 5vdc common? I would eventually like: 1. spindle speed override 2. feed rate override will this be possible with only input 12 left (assuming I didn't miss anything else)? I also see on the mpg pinout diagram that there is aux input 1,2,3 and aux output 1,2 - can these be used? If so, for what and what do the commons go to - 5vdc+ or 5vdc common? As I'm currently unemployed, I would like to avoid buying an input expansion board. Any further help you can give me would be greatly appreciated. I can't get a return email from Scott at Ajax (can't even get the stupid activation code so I can post on the Ajax forum )Thanks Again, Dave |
| Sponsored Links |
|
#11
| |||
| |||
| My advice is to just use the keyboard jog panel features for jogging, jog increment select, manual spindle start/stop, and so on. Once you get the machine up and running, and can make some money with it, buy the jog pendant. It will be an uphill battle all the way to try to roll your own operator panel without the benefit of an I/O expansion board. One of the nice features of the Centroid/Ajax control is the integration of the jog panel pendant. You get all the standard jogging, cycle control and machine control keys, plus programmable Aux keys, all in a unit that requires no extra wiring; doesn't occupy any of your PLC I/O; and takes little or no custom PLC programming. If $739 is out of the question right now, just use the keyboard features that are already available and reasonably functional. |
|
#12
| |||
| |||
| Am I really reaching that far? I thought I was pretty close to having all of this going. I've already made the control panel, mounted all of the switches and have them about half wired in. Whats mainly lacking is where to tie them in on the board. I know I will have to write brains for some of them and will need some help for any that are more complex than the simple cycle start/feed hold example from Scott. But I thought this was definitely do-able? If I forget about the feed and spindle overrides, am I in the ballpark on the rest? Thanks Again, Dave |
![]() |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | Search this Thread |
| Display Modes | |
| |
Similar Threads | ||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Mitsubishi DWC 110G Wire EDM Wiring Installation Assistance Needed | worldsworstfish | EDM Machines | 2 | 10-19-2009 10:03 PM |
| Newbie- Mitsubishi Servo and Drivers (HC-PQ a& MR-C).. problem wiring correctly | fcp | General Electronics Discussion | 8 | 12-10-2008 10:59 AM |
| Need Help!- Wiring for Mitsubishi AC Servo HA-FF Encoder | kumphanart | Servo Motors and Drives | 5 | 08-24-2008 01:30 PM |
| Need A Quote- Cable for Mitsubishi inverter Freqrol A 500 | Tahir Iqbal | CNCzone Club House | 0 | 07-25-2008 06:00 AM |
| MITSUBISHI FREQROL A500 INVERTER FR-A520-3.7K does anyone know if you can run 1 phase | CATCH22 | Phase Converters and VFD | 1 | 10-09-2006 12:19 PM |