Is this an older SERVO3IO system, then? If you have a DC3IO or DC3IOB, then you can set the 12 auxiliary inputs to use 24VDC sensors, in either a sourcing or sinking configuration. Be sure to remove the jumpers so you do not feed your external 24VDC onto the on-board 5VDC supply, and change out the three SIP resistors for 2.2K units if they are not that type already.The tool changer uses proximity sensors which require 24 volts. Since the PLC has 5 volt inputs, I have to put relays on all the inputs.