Timeout: 64180 not responding
Error occurred sending line 54 |
This is completely unrelated to the previous issues surrounding the E-stop contactor. This message indicates that the control software, running on the PC, did not get any response from the CPU7 board across the PC's ISA bus (expansion slot).
Try it again when the temperature is more reasonable. If you get the same message, open up the PC case; mark and unplug the five optical fibers; remove and reinsert the CPU7 board; return the optical fibers; and try powering up again.
The E-stop contactor will not close if the PC software has not started up successfully. That is because the PC software needs to start up the CPU7 board, and the CPU7 board needs to start talking to the servo drive, before the servo drive will close its RLY1/RLY2 terminals to complete the E-stop coil circuit.