Thread: New Machine Build What just happened???
View Single Post
  #7   Ban this user!
Old 06-29-2008, 07:33 AM
Ajax-oz Ajax-oz is offline
 
Join Date: Jun 2008
Location: Australia
Posts: 18
Ajax-oz is on a distinguished road

Originally Posted by mulligan View Post
The only change this time was I fired the cutter with the tip touching the table and the torch ground clamp was left hanging on the plasma cart...
That will cause you problems nearly every time.

Something to remember with anything electrical is that the current is trying to get to ground as fast as possible.

So when you left the plasma ground lead off your cutting table the current found another way to ground. It just happen to be through your drive motors to the controllers.

What you are planning on doing to improve your system looks good.
This is my thoughts.

Originally Posted by mulligan View Post
1. Earth ground attached to torch chasis and driven 4' into the ground. (Have done this already, BUT this ground rod is within 3' of electrical panel rod)
Originally Posted by mulligan View Post
Originally Posted by Ajax-oz View Post

Is your cutting bed, part of the CNC gantry

Yes. I have the typical 5/16 roller blade bearings for the gantry rollers.
Excellent
attach ground to the your cutting table.
The Gantry concerns me may need to have a ground connected to it as well. It would depend on the design.

Cable the that same size (or larger) as the earth on your plasma unit would do. I like using the flat braid for earths but they aren't convenient to use over longer distances.

Remember you still need to connect your earth from your plasma unit to the cutting table. The extra earths protect your electronics and you form being fried.

Originally Posted by mulligan View Post
2. Wire sheathing covering the torch lead from chasis all the way to handle on the gantry.
Excellent
Helps reduce RF

Originally Posted by mulligan View Post
3. Move all my electronics (drives, power supply, Print port protecter, etc) into a steel weather proof enclosure. Should this be case be earth grounded also? Currently and I am ashamed to say, everything is mounted on a temp sheet of plywood...
Excellent
Mount your steel weather proof enclosure to your chassis if you like.
Yes it should be earthed
I normally have a braided earth strap from the enclosure to the chassis, even if it is directly bolted.
Remember to remove the paint for the earth

Originally Posted by mulligan View Post
4. Rubber mount my motor mounts on my table. Since I have a timing belt setup, will this be sufficent for isolation?
Not needed in my opinion
Motors need to be grounded as well.

Originally Posted by mulligan View Post
5. Ensure that ALL grounds terminate with my power supply ground.
If you do as you said in number 3 this will be done in your steel weather proof enclosure.

Originally Posted by mulligan View Post
6. Ground only one end of the wire shields.
excellent

Originally Posted by mulligan View Post
7. Enclose torch case in a steel box if necessary?? The torch has its pilot arc in its case unlike my Hypertherm 600 which has it at the torch tip.

Should I switch to the hypertherm cutter??
I think it will most likely not be needed, but I could be wrong.
I work on the Hyperthem & Kaliburn (Inner Logic) 200A + units, so I don't now anything about the models you are talking about.

Here is a link to some of the equipment I work on
http://www.profilecuttingsystems.com/pcsproducts.html

Originally Posted by mulligan View Post
I have an aluminum block the compresses around the ceramic cup on my torch handle for a torch mount. This block is mounted to a piece of HIWIN rail and then to HIWIN bearing blocks.
It sounds like your torch is isolated nicely.

hope this helps

AJ
Reply With Quote

 

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361