Originally Posted by MarcL View Post
No evidence of a damaged or failed board. Right now it sounds like power is not getting through your E-stop contactor, either because the contactor is not closing or because the contact points inside are burnt or damaged.

When you press and release emergency stop on the console, do you see and/or hear the contactor clicking in and out?

The UV and USV lights on the servo drive indicate the presence of the motor power supply (ca. 120 VDC on terminals 9 and 10, "Gnd" and VM). This power comes through the E-stop contactor, so the UV and USV lights should go out when you press E-stop, and should come back on when you release E-stop and allow the contactor to close.

If the contactor clicks in when you release E-stop, but the UV and USV lights stay out, but you can make them come on by pressing on the contactor with a dowel, then you probably have burnt contacts inside.

If the contactor does not click in when you release E-stop, then you need to continue looking at the 24VAC loop.
this might sound funny but on some of the Semians - Irion controlers we have in our machines I have found that the crimp on the wire terminal was bad and recrimping to get a good connect worked , as far as the 24 volts in the contactor I have found the coil can't take much load at dead stops and get fried for some reason- so I always have a replacement till I can determine if the unit is bad , to keep me up and running. I feel the back BEMF spike takes them out in the hard shut down. just a thought. PS is the contactor in 2 parts the relay and the coil the coil part has a built in current limiter and that can be replaced the contactor is a seprate part and that can be replaced too if you have a gren lite that shows the cuirct is good and the coil has no voltage to pull contactor , I would check the coil and there is an adjustment to incress the current , is it a 2.6 or lower contactor ?
Reply With Quote

Sponsored Links
 

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361