What is the exact sequence of events during this operation.

Does it rapid travel to the cut,and along the way it will come down and sense the material and try to pierce? What happens when it gets to the cut? Does it stop the torch, move it to the home position at the top? Does it come down and sense the material again and cut out the shape? At the end of the cut does the Torch retract to it's home?

This is why a phone call is the best way to trouble shoot this type of a problem, due to the fact that there is a lot of different possibilities depending on the answers to these questions.

Due to the specific question of it is coming down and sensing the material during the rapid travel, I can come up with a few conclusions, and I will list them below.

A) The software is activating the output line during a rapid travel feature, most likely a software setting if it is 100% consistent, every rapid travel movement. Since you say it does it when it is just sitting there not running code, I would say that it is not the problem.

B) The plasma interface relay box itself is activating the height control, regardless of signal from the signal generator, test by turning the signal generator off or unplugging the output connector and see if it still randomly fires while sitting idle. If it no longer does, the output lines in the signal generator may be defective and outputting voltage when it is not supposed to be. To test that theory we would test with a multimeter the output line for +5v DC. If the signal generator was outputting this 5v randomly without being activated by the software, the problem I would say is the signal generator.

C) The relay itself is activating and telling the height control to activate regardless of input from the signal generator. Test by hooking a continuity tester or the ohm setting on your multimeter, to the back of the relay box to the two small screws. Unplug the relay box from the signal generator, and unplug the wires going to the start input on the height control. If it randomly activates the relay (should have a loud audible clicking noise) with no input, and no connection other then power, it would be a defective interface box)

D) If with the plasma interface box disconnected from the start input, you have the AVHC unit powered on and it randomly activates, goes down and sense the material, and fires the torch, then the problem would be with the AVHC box itself.

The key factor to all of these conclusions is that the AVHC unit is receiving the fire signal (closed loop) from the system with no input from the software. It could simply be a loose wire hanging in the wind, and that the software is activating the output line in between cuts. You think since it is a firing issue they must be related, where perhaps it is not. Let me know what other questions you need answered
__________________
Mike @ Torchmate.com | www.Torchmate.com
Toll Free : (866) 571-1066 M-F 7:30am-4pm PST
Reply With Quote

 

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361