There are a litany of problems with trying to resurrect an old VFD.

The first and foremost one is that if the VFD has been unpowered for any length of time, i.e. over a year, chances are that the capacitors will be toast shortly after energizing them. If you have a variable transformer you may be able to "reform" them by slowly increasing the voltage over a period of hours, but even then it may not work if the electrolyte has already dried out. On top of that, the generally accepted lifespan of a capacitor is 5-7 years. Yours are 20 years old! Once the caps are gone, the replacements would be more expensive than buying a new drive.

Problem #2 is the fact that all of the little caps on the PC boards are also old and likely to fail.

Problem #3 is that in most cases, a 480V drive cannot accept 240V 1 phase as an input, it will likely trip off on Low Voltage and/or Phase Loss even if you manage to get it to energize. In 1987 I doubt that AB even bothered giving you an option of disabling the LV/PL protection as some mfrs do now, because they never considered the possibility of using it as a phase converter, especially on a 480V drive. Most of ABs current drives will not allow you to do that.

The last problem I can think of is the Darlingtons. They are not likely made any longer, so if you manage to find some, they will be very very expensive.

Then there is a problem with what you want to do in general. A VFD does not make for a good 3 phase converter for powering a facility. The act of switching a motor on on the downstream side of the drive puts a tremendous strain on the transistors, what is called a di/dt surge (di/dt stands for delta-current over delta-time). Each time you do it, even if the transistors survive, you are doing incremental damage to the silicon substrates. In essence you are chipping away at their life span and it usually takes only a matter of months for them to fail, if not sooner. If you want to produce a 3 phase system for distribution throughout a shop, use a rotary phase converter. If you want 1 converter for 1 motor, use a VFD.
Reply With Quote

Sponsored Links
 

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361