Answering my own question: I talked to Hitachi and they said that the "current setting" is the same as the "full load amps". They reccommended that I leave the setting at the default of 8.0. They also had some specific setting recommendations for an inverter powering a milling machine:
Parameter A042 set to 00 (manual torque boost)
Parameter A044 set to 00 (constant torque)
Parameter A081 set to 01 (automatic voltage regulation)
Parameter B130 set to 01 (over-voltage LADSTOP enable)
Originally Posted by bilinghm I am doing the basic programing of the Hitachi SJ200 and have hit a snag. One of the parameters that must be set is referred to as "setting the motor current". The Hitachi manual says that The motor's current rating will appear on the manufactureres name plate. I can find no such current rating. Is there another term for this parameter? Could the equivalent Leeson term be "P.F."? P.F. appears on the nameplate and is shown as 85.2.
Bill |