Generally the philosophy behind the E-stop circuit has been for initially the protection of the operator, followed by protection of the machine itself, if one is building/retrofitting a machine for one's own use then pobabally anything goes, but if you are retro-fitting for a customer or have employees that are going to use the machine, then it would be a wise decision to look at the state & provincial codes and recommendations for legal reasons.
In the states there is the OSHWA and the NFPA regulations to consider, in Canada, there is usually Provincial regulations.
Going back to the original question, I tend to stick with the NFPA guide lines and use hardwired E-stop control and have software input to acknowledge the E-stop, rather than have the E-stop software originating it , which goes against the code.
First I set up an E-stop relay circut that has contacts to switch the servo amplifier-enables as well as remove the amplifier power, this relay would also control the spindle, and depending on what type of spindle would depend the degree of control i.e. standard AC induction motor, DC or AC Electron control or VFD. all require a different approach.
I also include the Watchdog relay on the Galil card in the E-stop string and the amp enable outputs on the Galil can be included AMPENX,Y,Z etc , Also I use the E-stop relay to switch off the power to all the logic outputs, the inputs I keep powered for diagnostic purposes especially if these are low voltage (5v to 24v ) type.
An input (e-stop) can be fed into the logic indicating a E-stop exsists, which inturn would be included in the FeedHold logic. And any other logic that was deemed necessary including issuing a Alarm message.
In some amplifiers such as DC & AC servo's, removing the DC power is not always sufficient to stop the servos as the DC supply remains charged for a period of time and can allow servo movement until the DC has decayed, that is the reason for also using the amp enable signals which most amps have.

Remember in an emergency the E-stop button is smallest button on the panel
Al
Reply With Quote

 

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361