Limit switch 101

Hello,

There are three types of axis "switches" used in cnc; soft limits, hard limits, and home switches.

Hard limits are the widest set apart, do NOT connect to the software--except to let it know, "Houston, we have a
PROBLEM!" In other words, these are electrically wired to shut things down safely regardless of what the computer or software might "want"... (Note that shutting down safelymay be MORE than just dropping the power immediately. Think of what will happen if a cutter is engaged in the cut when you power down the only thing--the drives--holding it in position. Climb cutting anyone!?!?

Inside of the hard limits are two more switches called soft limits. These are what has been described in the answers so far... Think of them like the "warning track" in a Baseball outfield. They ARE wired into the computer, and generally stop motion from CONTINUING in the same direction. Most better controls WILL allow motion in the opposite direction, which is one answer to your question. Some controls require you to acknowledge the soft limit alarm/fault before allowing you to move off the switch.
Still others will have a toggle in the software which does the same thing.

Soft limits are also capable of being put into the computer control itself--without the REAL switches on the machine. This is becoming more common, because it is obviously less expensive.
It also better allows the computer to do one of the important things which distinguish soft limits from hard limits. Which is to decellerate and MAINTAIN position. (Hard limits just stop motion immediately, and you have to reset and re-home to get back to work.) When soft limits are part of the software in the control they are usually called stroke limits, or stored stroke limits.

And they require the third type of switch, which is the home switch, or switches. This is a single switch per axis, which is very accurate. On more expensive machines, the home switch is electrically "and-d" with the encoder index pulse for precise repeatability. ("And"ing means BOTH the index AND the switch have to be on for the circuit to register as truly actuated. It is a common digital boolean function.) The home switch "location" is used by the computer to determine "where" the soft limits--stored stroke limits-- belong.

So in an ideal machine, there will be 5 switches PER axis! (Remember that 3 are more common nowadays, due to the use of stroke limits for the soft limit function.) Even less expensive machines will use mechnical stops for the hard limits--you can get away with this ploy with steppers, b ut with servos you should have REAL hard limit switches AND mechanical stops!

Some machines will use one of the soft limit switches for BOTH the soft limit--at the home end-- and as a home switch. These machines will often have two computer imputs for limits; limit hi and limit lo. And even less expensive technique is to use 2 switches in one NORMALLY-CLOSED "loop", so only one computer imput is needed. This is very typical of many of the machines shown here in "the Zone"...

You DO want your limit switches to be NC--Normally closed. That way, if a wire breaks, it will be seen as a switch opening, and stop the machine. This also prevents themachine from starting when a wire has broken between uses of the machine. Switches CAN ALSO fail in the closed shorted mode, but this is less common, and most designs DO use the NC mode...

One consideration to give your limits is the ability to allow for over-travel. Especially the soft limits. Because the axis might be moving quickly when the switch is sensed and it will take a bit of distance to slow, then stop the axis. Try not to set up your switches so the machine can get "behind" them, however. This can lead to all kinds of "fun" things!

Hope this helps,

Ballendo

P.S. "Types" may not be the best word. There are many kinds of switches, and "types" here means their USE, not their construction or actuating methodology...
Reply With Quote

 

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361