Originally Posted by DennisCNC
^^ I measured the shop and it is 45' not 50' so thats a plus. I will use it move granite slabs around, from the cart to the saw and so on. Maybe my 3K lbs estimate is a little high. The slabs weight is 1,200lbs. max plus the winch, trolly, vacuum lifter, I think that will be another ~700lbs. So I think a better estimate would be 2,200 lbs. max load. This load will mostly be in the middle.
I can make the trolly support wheels farther apart to spread the load. If I happen to need to move something heavier i'll just use the forklift. With the over head crain one person can move the material around.
Dear Dennis,

unterhaus is right on the button with with comments on buckling.

If the top flange of the I beam is not restrained (ie prevented from moving sideways), and you have a clear span of 45 foot, the permissible bending stress for the beam will be far less that the nominal value for the steel. In order to get round this problem, you have to go for a larger section.

I have not done steel calculations for a while, but I thought I'd have a go.

My conclusion is that if the ends of the beam are not built in to something substantial, and if the top flange is not restrained, the major factor is keeping the bending stress to acceptable limits. If you have a beam of steel which has a basic permissible bending stress of about 23000 lbs per square inch, by the time you make allowances for the span and the lack of restraint, the actual bending stress that the beam can handle is down to about 6100 lbs per square inch under these conditions.

If my calculations are right (and it is possible they are not) you might consider this beam....

24" deep
9" wide

top and bottom flange thickness 11/16"
web thickness 7/16"
beam self weight 225 lbs per yard

The steel should have a basic permissible bending stress of at least 23000 lbs per square inch.

The total deflection at mid span (including that due to the self-weight of the beam) will only be a little over 1/4". The bending and shear stress are within limits but I have not checked for web crushing and buckling.

Finally, please don't go ahead and use this beam without getting a structural engineer to OK it. I can't afford the lawyers fees!

Best wishes

Martin
Reply With Quote

 

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361